thermocouple relay is their such????
mer
Dec 2009
Asheville nc
59
Hello again i've started another project and i have limited inputs and i need to read several kilns with one reader so my question is,,is their a relay made that can or could read thermocouple (j or K )wire through the relay or if anyone knows some sort of way to read several points with one reader im game to any idea thanks in advance..Mer..
I have been trying to find some locking thermocouple plugs, still had no luck with that.
However, one supplier I spoke to told me to use any connector I wanted to, as so long as there is no temperature differential across the connector it won't act as a cold junction and affect the measurement significantly in my application.
Whether this is true for all temperature ranges I don't know, but I would be tempted to set up a trial using any old relay you like to see if it does actually affect the measurement.
I,ll try but !
i have been trying to find some locking thermocouple plugs, still had no luck with that.
However, one supplier i spoke to told me to use any connector i wanted to, as so long as there is no temperature differential across the connector it won't act as a cold junction and affect the measurement significantly in my application.
Whether this is true for all temperature ranges i don't know, but i would be tempted to set up a trial using any old relay you like to see if it does actually affect the measurement.
i have connected thermocouple wire with a butt connector and has threw the reading off by 40deg...
What the supplier said is true. If there is no temperature difference between the connection points, there will be no error. Getting connection points to be isothermal (no temperature difference between them) can be problematic.
The scheme is functionally a de-multiplexor, many inputs to one output. There has to be no temperature difference between (+) & (-) terminals at both input and output.
You are practically guaranteed a temporary error if you are handling the connectors and the wire while crimping a connector terminal, you finish, and connect it. Your body heat has transferred to the wire/connector.
Drafts or circulating air in a panel can heat/cool some terminals and not others. Any temperature difference between the connection terminals is a direct error at the cold end of the thermocouple. Shielding the connection points from any draft of air, whether cooling or convection heat is a wise idea.
The polarity of the thermocouple wires has to match.
+ has to switch to +
- has to switch to -
You can be big errors by swapping polarity.
The type thermocouple wire has to be identical on both input and output. K to K, J to J, etc.
We use a similar situation here, multiple temp. probes into one analogue input. OEM used a multiplexer card, and this works very well in our situation
Hey all, Trying to find a small footprint adjustable temp relay with thermocouple input that is good for higher voltage DC. I have come across...
4,970
I am having an issue getting a IY4 to read my thermocouple correctly. We have a R type and K type hooked up and sitting at a known room...
567
Posted by u/mr_biodtox 44 minutes ago Delta ISPSoft - Establishing communication with thermocouple module Hi, How do I establish communication...
347
Hi, We have an ongoing project with a lot of thermocouple involved that monitor the temperature of heaters. There are more than 20 PID...
32
3,532
Hello. PLC beginner here, so apologies in advance for any incorrect terminology or poor communication. I have an SLC 500 Thermocouple/mV Analog...
659