Hey all,

Trying to find a small footprint adjustable temp relay with thermocouple input that is good for higher voltage DC.

I have come across the Siemens 3RS120 series relays but ideally looking for something even smaller if there is such a thing out there. Simply looking to turn off a heating element with built in thermocouple. Something nonadjustable could work as well if calibrated temperatures were in the right ranges like open @ 60-70°F.

Thanks
 
I usually use Watlow limit controllers, they come in size from 1/32 DIN up to 1/4 DIN but I usually pair them up with a contactor for switching the load.
 
How about a temperature switch instead. The output of this would feed your SSR to handle your high voltage.
https://www.automationdirect.com/adc/overview/catalog/process_control_-a-_measurement/temperature_sensors_-a-_transmitters/temperature_switches
Just a thought.
Regards,

Been looking for a temp switch option, it would need to be a surface/contact type but surface space is limited to under 1/2". Open ~15C. Seen a couple little guys that could be contenders but their construction and purchase sites seem a little sketchy.
 
Don't know about size of Siemens model you mentioned, but I have used few times Omron E5C2-K (K type TC), and it has size of standard 11-pin relay.
 

Similar Topics

I am having an issue getting a IY4 to read my thermocouple correctly. We have a R type and K type hooked up and sitting at a known room...
Replies
5
Views
532
Posted by u/mr_biodtox 44 minutes ago Delta ISPSoft - Establishing communication with thermocouple module Hi, How do I establish communication...
Replies
1
Views
338
Hi, We have an ongoing project with a lot of thermocouple involved that monitor the temperature of heaters. There are more than 20 PID...
Replies
32
Views
3,480
Hello. PLC beginner here, so apologies in advance for any incorrect terminology or poor communication. I have an SLC 500 Thermocouple/mV Analog...
Replies
1
Views
650
Hello Guys, Trying to scale a thermocouple directly into my IY4 card. Connected into the terminal +\-. I’ve scaled the range of my J type to...
Replies
4
Views
1,670
Back
Top Bottom