Kepware routing help

Kepware rookie...

For some OEE purposes, we are trying to collect data from a ControlLogix PLC. We have to go thru an another ControlLogix backplane to get there. We keep getting "invalid device id" errors. Is it possible? Is our format wrong?

The path we set is: <10.1.ww.yy>. 1. 2. 2 <192.168.xx.zz>. 1. 0

10.1.ww.yy is an EWEB card, to the backplane, out the ENET card in slot 2, to the other PLC. Seems right. Maybe not...

Thanks
Justin
  Reply With Quote
Old March 17th, 2023, 01:46 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,974
It looks essentially correct to me.

There should be a "." before the second IP address (but I assume you typed this out instead of copy/paste/edit).

Remember that ControlLogix slots start at the leftmost Slot 0. This assumes that your second Ethernet module is in the third physical slot (2) of its chassis, and that the target ControlLogix CPU is in the first physical slot (0) if its chassis.

Have you been able to navigate the same path with RSLinx Classic and maybe set up an OPC Topic, and use the Test Client ?
  Reply With Quote
Old March 17th, 2023, 02:59 PM   #3
stretch_af
Member
United States

stretch_af is offline
 
Join Date: Mar 2011
Location: Drinking in Wisconsin
Posts: 56
Yep, that path was typed out. I forgot the "."

I can drill down to the processor thru Linx.


Next question is DH+. The same 10.1 chassis has DH+ cards. Any pointers on what the format thru the backplane and out a DH+ card would look like?
  Reply With Quote
Old March 17th, 2023, 03:17 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 16,974
Unfortunately I'm not sure how Kepware navigates the 1756-DHRIO.

MSG instructions from PLC's are aimed at the DHRIO itself with a payload that says "execute a PCCC/DH+ command on this Channel, with this target node/gateway node/link ID, and give me the result". There's no CIP path that includes the channel/node/gateway/linkID.

RSLinx Classic basically does that behind the scenes and shows it in a graphical browse.

So this might be a Kepware-specific configuration question that I can't answer.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Kepware and RSView Studio 5000 martinshaw LIVE PLC Questions And Answers 10 July 18th, 2019 12:56 PM
cimplicity V9.0 talking to remote Kepware OPC server dogyi LIVE PLC Questions And Answers 1 March 4th, 2016 12:23 AM
BACnet communication between Kepware communication server 5.8 and BACnet Card. lalitvedak LIVE PLC Questions And Answers 0 December 23rd, 2012 12:03 AM
Change RACK ID on Kepware dynamically !! amitgolwala LIVE PLC Questions And Answers 1 June 30th, 2011 09:19 PM
Siemens STARTER and routing ethernet / profibus. JesperMP LIVE PLC Questions And Answers 2 April 29th, 2010 09:15 AM


All times are GMT -4. The time now is 05:08 AM.


.