5069 Module Firmware Flash Failure

Hi all,

I've been without luck flashing a 5069-HSC2xOB4/A module to anything higher than the onboard v1.050 firmware.

Has anyone else had luck with this module, or others in general?

The setup:
  • Controller is a L320ERM with firmware 32.14
  • Module is working, has firmware 1.050, and occupies slot 1
  • No other modules
  • MOD power good
  • SA power good

Approaches and tools tried:
  • Direct Ethernet and USB connections
  • Controller in remote run or program mode
  • Module inhibited in I/O tree
  • Module not inhibited in I/O tree
  • Module removed from I/O tree
  • Module inhibited in I/O tree and manually reset
  • 2.011 / 3.012 with latest ControlFlash
  • 2.011 / 3.012 with latest ControlFlash Plus
  • RSLinx Classic Gateway
  • FactoryTalk Linx
  • 2 hours of phone support with Rockwell (this included all of the above including a factory reset of the controller)

Furthest degree of success:
  • ControlFlash claims the module isn't in the correct mode to accept a firmware update, fails, then provides a pop-up "Manually Reset Module"
  • ControlFlash Plus immediately advances from 'Flashing' to 'Polling for Power-Up', then times out with error "Failed to begin update to the target device.The target device is not in the proper mode to accept an update.Manually Reset module"

Last edited by JeremyM; May 22nd, 2020 at 06:01 PM.
  Reply With Quote
Old May 22nd, 2020, 08:20 PM   #2
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 147
You have provided all options one could think of. Is it possible that there is an issue in the wiring of 5069-HSC2xOB4/A that causes it to detect a fault that does not allow firmware update? Is the 5069-HSC2xOB4/A wired to the physical IO?
  Reply With Quote
Old May 22nd, 2020, 10:50 PM   #3
JeremyM
Lifetime Supporting Member
United States

JeremyM is offline
 
Join Date: May 2014
Location: Texas
Posts: 414
No wiring, just attached to the processor.
  Reply With Quote
Old May 22nd, 2020, 11:31 PM   #4
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 147
So, the only thing I can think that you have not tried is to plug some real IO in case the lack of IO can generate an error condition that prevents flashing new firmware.
  Reply With Quote
Old May 23rd, 2020, 08:09 AM   #5
PreLC
Member
United States

PreLC is offline
 
PreLC's Avatar
 
Join Date: Apr 2019
Location: Mars
Posts: 93
In the manual: 5069-um006_-en-p.pdf for the compactlogix, on page: 29, it states that the firmware update request is rejected as long as the "Connection running" state is true.
On page 108 it also mentions that the LED on the controller must be flashing green to indicate that the module is powered and with no connection.

I would suggest erasing the program on the PLC(By doing a download and cancelling mid-way, or maybe pull the battery out?), then trying another flash?
Thanks!
-PreLC
__________________
Ask not what your PLC can do for you, ask what you can do for your PLC.
  Reply With Quote
Old May 23rd, 2020, 02:16 PM   #6
JeremyM
Lifetime Supporting Member
United States

JeremyM is offline
 
Join Date: May 2014
Location: Texas
Posts: 414
I’ll see if I can flash it while it’s installed among other cards.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
control logix module failure identification PSpal LIVE PLC Questions And Answers 1 September 17th, 2012 10:14 AM
Rockwell 1756-61 Firmware Upgrade Failure derama2 LIVE PLC Questions And Answers 9 April 1st, 2010 10:54 AM
ET200S Safety Module Failure bmw_apprentice LIVE PLC Questions And Answers 6 March 13th, 2010 02:32 PM
AB 1746-HS module - IMC 110 motion controller raj LIVE PLC Questions And Answers 12 February 20th, 2009 01:36 AM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 07:38 PM


All times are GMT -4. The time now is 04:47 AM.


.