paperboy4828
Member
Looking for some help with downloading to a Panelview 1400e via a SLC 5/04 and 1747-SN,B RIO scanner. The 1747-SN,B is configured for racks 0-3, all full racks. The Panelview is configured for a RIO passthru application at 230.4 baud. The 1747-SN,B is also configured for 230.4 baud. When an application is transferred to the Panelview via serial link, application transfers and communication with 1747-SN,B is fine. Block transfers work without fail. Communications are set up from PC to serial connection on SLC 5/04, 19,200 baud, on system channel 0. When trying to do a passthru file transfer, Panelview is setup through the touch screen for network transfer, RIO... When switched back into run mode, the 1747-SN,B presents a green blinking light, indicating that "at least one remote device is not communicating". I have tried to change the block on the Panelview RIO setup from 0 to 1 to 2 to 3 with the same results each time. Thru RSlinx, communication to the SLC 5/04 is fine. Channel 1 in the SLC 5/04 is setup as DH+, 230.4 baud, but is not used. If I load and start the DH+ driver in RSlinx, and look at RSwho, I see the serial network, the SLC 5/04; under the 5/04 I see the DH+ network, and the SLC 5/04 again. I'm assuming that is the DH+ on channel 1 that is not connected to anything. I can never seem to get the panelview to show up in RSlinx, and with out that communication the passthru will never happen. What am I missing here?