SLC 5/04 + 1747-SN,B passthru to Panelview
paperboy4828
Jan 2006
Upstate, NY
17
Looking for some help with downloading to a Panelview 1400e via a SLC 5/04 and 1747-SN,B RIO scanner. The 1747-SN,B is configured for racks 0-3, all full racks. The Panelview is configured for a RIO passthru application at 230.4 baud. The 1747-SN,B is also configured for 230.4 baud. When an application is transferred to the Panelview via serial link, application transfers and communication with 1747-SN,B is fine. Block transfers work without fail. Communications are set up from PC to serial connection on SLC 5/04, 19,200 baud, on system channel 0. When trying to do a passthru file transfer, Panelview is setup through the touch screen for network transfer, RIO... When switched back into run mode, the 1747-SN,B presents a green blinking light, indicating that "at least one remote device is not communicating". I have tried to change the block on the Panelview RIO setup from 0 to 1 to 2 to 3 with the same results each time. Thru RSlinx, communication to the SLC 5/04 is fine. Channel 1 in the SLC 5/04 is setup as DH+, 230.4 baud, but is not used. If I load and start the DH+ driver in RSlinx, and look at RSwho, I see the serial network, the SLC 5/04; under the 5/04 I see the DH+ network, and the SLC 5/04 again. I'm assuming that is the DH+ on channel 1 that is not connected to anything. I can never seem to get the panelview to show up in RSlinx, and with out that communication the passthru will never happen. What am I missing here?
passthru to panel view
hey go in through Rslinx and change the driver config from the slc-ch0/microview/panelview to the driver for 1770-KF2/1785-KE/SCANport
that will at least get it to show in rslinx and then in rslogix make sure you change in the Processor status tab goto ch0 and change thedf1 pass-Thru enable bit to 1.
I have done as you suggested, that exact same procedure that I downloaded from a Rockwell white paper. My current understanding is that the SLC5/04 ser.c is only capable of "one-hop" passthrough. That is, if the Panelview were setup on the DH+ network, the above procedure would work fine, but with the Panelview setup through a RIO card (1747-SN,B) the proper passthrough link can't accessed.
The answer is to communicate using my PCMCIA DH+ communication card directly to the DH+ port on the SLC5/04, which can then see nodes on the RIO network. What I was trying to do in the first post is not possible due the limitation of the "one-hop" passthrough.
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,610
I have the following Items connected for DH-485 per the drawing. SLC 5/03 HMI: Automation Direct EA9-T10CL+13Y19B054 1747-AIC #1: connected...
3,049
Hello, First I looked at Manuel and Plctalk but I did not find or maybe not understand. How I can connect ''HTL / Push pull-24 volt encoder'' to...
2,526
Hello I will make it short and sweet. I need the cable that goes from the slc 501 to the 1747-UIC RJ-45 connection. From what I can find it...
1,250
All, Thanks for any help. I am currently changing out an 1747-L543 processor over to an 1747-AENTR card so that I can now run this rack from an...
2,114