Hi everybody,
I have a CLX system with 2 redundant 1756-L71.

Our customer requires two values: "CPU1_OK" and "CPU2_OK" to be sent via modbus (using Prosoft PLX31-EIP-MBS gateways).
CPU1 and CPU2 means Chassis1/Chassis2 and not Primary/Secondary.

I was thinking of providing them this way:
1) by using GSV - REDUNDANCY - PhysicalChassisID determine which controller is the primary
2) by using GSV - REDUNDANCY - PartnerChassisRedundancyState
determine if the secondary cpu is OK (any state other than SYNC means 'false')

but what about the primary cpu ?
I was thinking of using a Fault Routine to detect any problem on the primary cpu.
But in this case how this will work with the switchover ?
Will this only work when the secondary CPU is DISQ ? (which means that both CPU1_OK and CPU2_OK will be false)


Thank you for your support.
 

Similar Topics

Controller: 1756-L84E v.35 Prosoft MVI56E-MNETC for ModbusTCP/IP I'm having an issue with some of my write commands. The write command that...
Replies
0
Views
195
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
Replies
2
Views
420
What's the best way to move a tag value from the panelview+7 to the clx plc. We display amps from a power meter on the panelview screen, read in...
Replies
1
Views
398
I'm running into an issue migrating a PLC-5 using the newer Logix Designer Export when opening a saved .ACD from RSLogix-5. It has multiple RIO...
Replies
2
Views
617
We have two sites that are stranded with no line of site, they are handled by phone/modem with a chain that includes: Stranded site (client)...
Replies
5
Views
909
Back
Top Bottom