Strange RS-232 scanner to PLC noise problem

So I had a strange problem today that defied what I've learned about data communication.

basic setup is: Scanner -> PLC via RS-232 using only the Tx, Rx, and GND at 9600/8/None/1

Basically what I saw was that whenever any of the VFDs for the motors where running, my scanner read rates went to hell. But the RS-232 connection continued to work fine. The PLC read the bad-scan data with no problem.

I finally resolved the problem by connecting the shield for the RS-232 line to earth ground on both ends. I was grasping at straws by the point I tried this and just happened to get lucky.

This makes no sense to me. Doesn't this create a ground loop? I've always heard to only connect the shield to earth ground on one side to properly eliminate noise and never on both ends.

I almost have the feeling that the scanner which is on a seperate 120vac circuit isn't grounded properly and by hooking up the ground on both ends I was providing the scanner a proper ground but I really have no idea. I have a scope meter, but am pretty clueless with what I'm looking for as far as detecting line noise.

Any info you kind fellers have on the subject would be greatly appreciated.
  Reply With Quote
Old April 19th, 2005, 06:29 PM   #2
Eric Nelson
Lifetime Supporting Member + Moderator
United States

Eric Nelson is offline
 
Eric Nelson's Avatar
 
Join Date: Apr 2002
Location: Randolph, NJ
Posts: 4,346
Quote:
Originally Posted by monkeyhead
I almost have the feeling that the scanner which is on a seperate 120vac circuit isn't grounded properly and by hooking up the ground on both ends I was providing the scanner a proper ground but I really have no idea.
That sounds like a reasonable conclusion. Now, assuming that this IS the reason, you'll want to find a way to 'properly' ground the culprit. IOW, I wouldn't rely on the shield ground as the ONLY path to ground...



-Eric
  Reply With Quote
Old April 19th, 2005, 06:37 PM   #3
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 10,002
I once looked into grounding, and whether or not both ends of a shield should be connected depends on the frequency of the noise and of the voltages being used in the vicinity. For frequencies in the 60 Hertz range, calculations (and experience) show that one end is better, and for 300 Hertz frequencies (as I remember), both ends grounded is better, as far as noise elimination is concerned.

The ground-loop problem is another issue that should be handled with proper grounding on all power circuits before the control circuit noise issue is addressed.

Last edited by Lancie1; April 19th, 2005 at 06:41 PM.
  Reply With Quote
Old April 19th, 2005, 06:42 PM   #4
monkeyhead
Member
United States

monkeyhead is offline
 
monkeyhead's Avatar
 
Join Date: Sep 2004
Location: I'm right here
Posts: 656
Red face

I'm almost hoping that's not the solution, because I checked the ground for the 120vac circuit until it headed up to the ceiling and everything looked good. But who knows how many other circuits are sharing that ground... the distribution in our building is a mess and completely undocumented. i have a plug with the ground tied to the hot that I use as my circuit 'tracer'.
  Reply With Quote
Old April 19th, 2005, 07:14 PM   #5
monkeyhead
Member
United States

monkeyhead is offline
 
monkeyhead's Avatar
 
Join Date: Sep 2004
Location: I'm right here
Posts: 656
Quote:
Originally Posted by Lancie1
The ground-loop problem is another issue that should be handled with proper grounding on all power circuits before the control circuit noise issue is addressed.
you just cleared up a lot of confusion for me with this statement. now i need to go slap my data com instructor for not understanding the material he was teaching.
  Reply With Quote
Old April 19th, 2005, 08:12 PM   #6
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,299
Although every situation is unique, (and no matter what I say, there will be 427 other opinions)... It seems that in GENERAL, manufacturers recommend grounding 'signal' leads, be they pulse train (encoder), or analog, at one point and one point only, while they recommend grounding 'Data Transmission' leads everywhere.

There are NOTABLE exceptions to the guidelines though... Controlnet, for instanct, should NEVER have it's outer shield conductor grounded. Ethernet twisted pair cable should be unshielded if both ends can't be grounded (UTP), or shielded (STP) if both ends can be bonded to ground at an appropriate connector. One grounded and One ungrounded end on STP cable will work, but will cause major data errors (invisible except for network slowdown) at 100MBps and over. Go figure.

Best advice (even though it sucks), is follow whatever the MANUFACTURER of your device recommends. Failing to do that will often (cough Rockwell, cough Siemens) result in a "No Support" policy.
  Reply With Quote
Old April 19th, 2005, 10:09 PM   #7
monkeyhead
Member
United States

monkeyhead is offline
 
monkeyhead's Avatar
 
Join Date: Sep 2004
Location: I'm right here
Posts: 656
holy wow... i've just spent the last couple hours researching all this ground loop / inductance / noise stuff. and although more knowledgeable on the subject, i'm still just as confused.

but what i've come to realize, is the problem is the noise is disrupting the internal communication of the scanner and not the RS-232 connection between the PLC and Scanner. so right now i'm thinking that by connecting the two frame grounds via the shield i'm actually re-directing the noise to the cabinet's ground instead of through the scanner's electronics. but the noise is not great enough to distort the rs-232 signal.

kinda makes sense to me since EIA-232 states that 1's range from +3v to +15v and 0's range from -3v to -15v and are fairly discreet, where in contrast the scanner decodes the analog signal from the optical reciever and that circuit is probably much more prone to noise disruption.

who knows... i'm gonna run a nice fat conductor between the scanner's frame ground and the PLC cabinet's frame ground and disconnect one side of the shield and see if it has the same effect. if it does i'll test accross the two grounds and see if i've got potential and then call it a ground loop problem.

my brain hurts.
  Reply With Quote
Old April 20th, 2005, 04:05 AM   #8
Andybr
Member
United Kingdom

Andybr is offline
 
Join Date: Oct 2004
Posts: 587
This does not sound like a comm's problem at all to me. It looks more like a problem with the trigger input on the scanner. Most of our scanners are triggered by a PEC which is connected to an input on the scanner. This input can usually be turned on by even a very low voltage and it would certainly be possible for noise to trigger false scans. It may be that the additional earthing you are providing is helping to prevent this but since the scanner is still transmitting bad read messages the RS232 part of the system must be working correctly.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PC to PLC Protocol TheRixta LIVE PLC Questions And Answers 13 December 17th, 2008 01:56 PM
Rs 232 / Tcpip Converter mahdi_rtt LIVE PLC Questions And Answers 5 November 24th, 2004 08:55 PM
I/O Comm. problem btw PLC & HMI WFox LIVE PLC Questions And Answers 7 December 31st, 2003 02:09 PM
PLC5/40 Backplane Problem????? Andrew Evenson LIVE PLC Questions And Answers 18 August 24th, 2002 08:06 PM
PLC + Motor Problem Ken LIVE PLC Questions And Answers 4 July 30th, 2002 10:17 PM


All times are GMT -5. The time now is 05:06 PM.


.