Rockwell 1734-ie2c problem

buoanventura

Member
Join Date
Jun 2011
Location
italy
Posts
5
Hi Guys,

We Have some problem with 1734-ie2c module with controllogix cpu, sometimes the input value went to 0 without Module alarm.
suggestions? 🤞🏻
 
What type of error are you expecting? I would check the configuration. You're probably set for 0-20ma instead of 4-20ma. (Assuming you're anticipating an out of range error)
 

Similar Topics

HI All, I would like to know your opinion about the disposition over the 1734 and 1718 rack for the I/O Cards. - Normally I use for the first...
Replies
1
Views
485
Rockwell PLC with 1734-4IOL/A IO-Link Master communicating to 3rd party device. Devices without Premier IODD files normally only have a device...
Replies
0
Views
1,320
Hey there, I see lots of people have had issues over the years with the AENT's. The old series A basically stop doing anything over the network...
Replies
5
Views
2,473
Hi there, Long time lurker posting for the first time. TLDR: Trying to configure a small Point IO drop into an existing system, the point IO...
Replies
23
Views
27,395
Hello all, I am an Industrial Electrician, and deal with a little bit of everything including PLC troubleshooting and programming. When I started...
Replies
3
Views
137
Back
Top Bottom