PanelView 550 touchscreen problem

thanks

i already do that, but not success, the PV error msg is erorrr fehle fehle... after i press both Left and Right Arrow keys
 
Check the communications cables and settings first; did you replace anything or reconfigured prior to the fault condition?

If it went Offline while running you might need to replace it if everything else checks out.
 
i think i changes the baud rate but i forget the value, how to connect HMI to PC, i have Allen Bradley Micrologix 1761-CBL-PM02 SER C Pc To Micrologix Comms Cable and also Allen Bradley Slc 500 1747-UIC USB To DH485 Converter, can i do connection with that cable?

thx for help
 
What PLC type is the HMI connected to?
Do you have a 1761-NET-AIC interface between the terminal and the PLC?

For ML 1000, 1200 and 1500LSP straight connection you will need a 2711-NC21 or 2711-NC22 cable; if you have an AIC+ interface you will need a 2711-NC13 or 2711-NC14 cable from the PV to the AIC+ and a 1761-CBL-HM02 from the AIC+ to the controller.

For SLC, PLC5 or ML1500 LRP you will need a 2711-NC13 or 2711-NC14 cable.

Your HMI is communicating over DF-1 Serial.

The default communications setup for the terminal is as follows:

No Parity
8 Data Bits
1 Stop Bit

Baud Rate = 9600

Node # = 64

Error Detection = CRC

Handshaking = OFF


These settings need to match the controller's Serial DF-1 port settings.
 

Similar Topics

Hi all, Im having trouble transferring a program from one panelview 550 to an new one. I can insert a flash card into the old panelview and upload...
Replies
20
Views
348
Client has multiple spare Panelview 550 (2711-T5A10 L1 PV550 Touch Devicenet)...
Replies
5
Views
688
need instruction on how to download an existing program to the PV. I am very new to PLC's they came with the job so now sink or swim don't want to...
Replies
6
Views
908
Good afternoon I have a panelview 2711-k5a2 ser B Rev-C frn 1.07. Can this be up graded to Rev J frn 4.10-4.XX? Thanks
Replies
17
Views
3,433
Panelview 2711-K5A8. Customer has 6 of these in service connected to SLC 504’s. One has a bad backlight and I need a solution to replace it...
Replies
11
Views
2,257
Back
Top Bottom