PanelView 550 touchscreen problem
dwg
Oct 2003
Has anyone had problems with thier touch screen getting dead spots
in the upper portion of the screen? Is this always a hardwareproblem? I'm having repeat problems with this on different machines. I can replace the unit with a rebuilt one and it will
work for a few days to a few weeks, then the touchscreen stops responding to touch in the upper part of screen. Reloading the program does not fix the problem.
I have also same problem but it is middle or some time whole touch screen not working. Pl. suggest.
Upgrade it. It is a hardware problem, and that hardware is obsolete (assuming you're dealing with a PanelView standard).
Tell us the complete part number of your HMI so we can assess your options.
Pretty common on the 550's
If it is a model with key pad as well as touch just reconfigure the application to use the F keys instead of the touch pad.
If no keypad, you can move the items in the dead area to areas that are not and then reload the revised application.
Best scenario though would be to upgrade to a more modern panel.
BCS
BCS
There is only touch pad
Ugh, having ControlNet communications means that any replacement will have to take advantage of a different means of connecting to the PLCs with which it reads and writes data. Unless there is a modern replacement HMI that supports ControlNet that I am unaware of
So the next question becomes what device(s) must this HMI communicate with?
communicating via ControlNet.
There are several 2711-T5A15L1 units available in the open market.
If you want to upgrade, you can also purchase a Panelview Plus with A 2711P-RN15S module (controlnet module).
You attach the 2711P-RN15S module to any PanelView Plus, voila, you can connect your PLC to the PV+ controlnet.
Help!!!
help me with PanelView 550 touchscreen error 686 panelview offline, and cannot enter configuration setting.
thx
Your HMI is not connected to the PLC.
Turn terminal power Off and then back On with both Left and Right Arrow keys pressed; when in the configuration screen verify the communications setup on both the HMI and the PLC.
Hi all, Im having trouble transferring a program from one panelview 550 to an new one. I can insert a flash card into the old panelview and upload...
20
353
Client has multiple spare Panelview 550 (2711-T5A10 L1 PV550 Touch Devicenet)...
690
need instruction on how to download an existing program to the PV. I am very new to PLC's they came with the job so now sink or swim don't want to...
909
Good afternoon I have a panelview 2711-k5a2 ser B Rev-C frn 1.07. Can this be up graded to Rev J frn 4.10-4.XX? Thanks
17
3,435
Panelview 2711-K5A8. Customer has 6 of these in service connected to SLC 504’s. One has a bad backlight and I need a solution to replace it...
2,257