Help with Circuit (Control Reliable)
Okay,
So I'm designing a motor circuit that will have E-stops running to a AB safety relay.
What keeps the Contactor that the safety relay will pull in safe? How do I prevent a contactor from becoming welded?
I've went over some historic drawings of other machines I've seen and the safety relay is always force guided and control reliable, but it always seems as if the contactor were welded shut, nothing would ever know.
Thanks in advance!
Old February 9th, 2018, 02:15 PM   #2
jstolaruk
United States
jstolaruk is offline
Check out A-B's safety contactors http://ab.rockwellautomation.com/Mot...ors/IEC/Safety
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
Old February 9th, 2018, 02:16 PM   #3
g.mccormick
United States
g.mccormick is offline
Put two contactors in series.
Old February 9th, 2018, 02:25 PM   #4
mk42
United States
mk42 is offline
Quote:
Originally Posted by Timeismoney08 View Post
Okay,
Thanks in advance!
Generally, you use TWO contactors, so that if one welds shut, the other will still break the circuit. You should also be using contactors with an auxiliary feedback contact, to report status back to the system/safety relay.
I believe it is usually required to have a periodic test carried out (once a shift, once a day, once a week, depending), to check for hidden faults. This is often procedural, not automated.
Old February 9th, 2018, 02:26 PM   #5
Timeismoney08
United States
Quote:
Put L1,L2,L3 through one contactor and then through another contactor in series. Then to pull in that contactor, have the output side of each chain on the safety relay pull in each contactor individually and monitor the AUX on the PLC?
Would the PLC need to be safety rated at that point to monitor for a stuck contactor? and would that make it control reliable as long as there is no one point of failure that could trick the system into always running?
Thanks!
Old February 9th, 2018, 02:31 PM   #6
Timeismoney08
United States
How do you monitor the two contactors in series with a safety relay if they only pull in when it's in a safe condition? Would I need 1 Safety relay for the E-stops and 1 for the Motor/Contactor Circuit? Could I use Auto reset on that safety relay just for the contactors?
Old February 9th, 2018, 02:31 PM   #7
jstolaruk
United States
Thanks!
No the safety relay should have those monitoring inputs.
__________________
Old February 9th, 2018, 03:02 PM   #8
g.mccormick
United States
The reset for the estop relay would go through the two NC contacts on the contactors in series. So that both of the contactors have to be off before the estop can be reset.
Old February 9th, 2018, 07:29 PM   #9
Timeismoney08
United States
Genius! Thank you everyone for the help! I was sure there was an easy solution.
What if the motor being controlled didn't cause a danger? Would I still need that high level of guarding?
Thanks!
Old February 9th, 2018, 08:47 PM   #10
PLCnovice61
Australia
PLCnovice61 is offline
Its unlikely that the motor parse would cause a danger, it is the machinery that the motor is driving that would be the possible danger. The best/correct method is to have done a risk assessment and then do the circuitry to the level require to meet assessed danger level.
Old February 10th, 2018, 06:51 AM   #11
sparkie
United States
sparkie is offline
Thanks!
You are on the right track by by analyzing the system for potential safety concerns. I think about safety before I ever start, and then again, afterwards.
You can't always design to the maximum level of safety, there is always a trade-off, and as the designer of the system, it is up to you to to determine where they meet. You want to build a solid-reliable system that is easy to troubleshoot, will not hurt anyone, and is as safe as it needs to be to protect people. A wise man once told me:
1. Operator safety
2. Product quality
3. Production Efficiency
Old February 14th, 2018, 11:17 AM   #12
mk42
United States
mk42 is offline
The feedback should go to whatever device is controlling the contactors. That COULD be a safety rated PLC, but could also be a safety relay, or something else like a safety drive.
Old February 14th, 2018, 11:35 AM   #13
AustralIan
United Kingdom
AustralIan is offline
Read ISO 13849 for how to do risk assessments and implement appropriate safety circuits to mitigate the risks identified.
A single contactor can be ok for a hazard requiring PLc mitigation.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
what is motion control with PLC backendcode LIVE PLC Questions And Answers 1 November 2nd, 2017 04:26 AM
Beginner in Panel Builder for PLC budiman LIVE PLC Questions And Answers 8 November 29th, 2013 05:04 PM
Motor Ground Fault Short Circuit protection question russrmartin LIVE PLC Questions And Answers 16 March 5th, 2006 01:50 PM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 11:57 AM
grounding power sources drewcrew6 LIVE PLC Questions And Answers 18 December 12th, 2002 06:16 PM