Old February 13th, 2018, 10:45 PM   #1
mjellison
Member
United States

mjellison is offline
 
Join Date: Feb 2018
Location: Amesbury, MA
Posts: 2
Unhappy Need to Restore PLC w/ Wiped Memory

Hi All,

We are using a MicroLogix 1400 PLC in a double-sided lapping machine at my work. Unfortunately while the breaker switch was turned off, the lithium ion battery got unplugged which wiped the memory in the PLC.

I believe I have found a backup file, but it is in .xml format. Would it make sense that one of these files would be in the .xml file format? If so, how do I convert the file back into something that I can upload to the PLC? Do I need to purchase RXLogix 500 in order to do this, or is there a free program that I could use?

Thank you for any help you can provide me.
  Reply With Quote
Old February 13th, 2018, 11:05 PM   #2
scarince
Lifetime Supporting Member
United States

scarince is offline
 
Join Date: Jan 2009
Location: Dayton, OH
Posts: 121
You will need RSLogix500, there's no way around that.

The file suffix you need should be a .RSS file. The .xml file might be something you can use, but someone more knowledgeable than I will need to weigh in on that.

Good luck!!
  Reply With Quote
Old February 14th, 2018, 12:40 AM   #3
Logix_Stef
Member
United Kingdom

Logix_Stef is offline
 
Logix_Stef's Avatar
 
Join Date: Oct 2014
Location: Havant
Posts: 83
Try a local Rockwell Service Center, they can send a field engineer to upload the program. Doubtful that the *.xml file will help, sounds like an MS Excel file to me.
  Reply With Quote
Old February 14th, 2018, 03:02 AM   #4
Rob...
Supporting Member
United Kingdom

Rob... is offline
 
Join Date: Jul 2016
Location: Manchester
Posts: 142
Quote:
Originally Posted by Logix_Stef View Post
Try a local Rockwell Service Center, they can send a field engineer to upload the program. Doubtful that the *.xml file will help, sounds like an MS Excel file to me.
If the CPU's memory has been cleared due to the battery being taken out, there will be no code to upload.

I haven't seen a way of converting an .xml file back to a .rss. Unless someone on here can correct me.
  Reply With Quote
Old February 14th, 2018, 03:09 AM   #5
Logix_Stef
Member
United Kingdom

Logix_Stef is offline
 
Logix_Stef's Avatar
 
Join Date: Oct 2014
Location: Havant
Posts: 83
Quote:
Originally Posted by Rob... View Post
If the CPU's memory has been cleared due to the battery being taken out, there will be no code to upload.

I haven't seen a way of converting an .xml file back to a .rss. Unless someone on here can correct me.
me neither. The program will have to be re-rwitten from scratch or the OEM to be contacted for the source file. Damn situation, been there myself a coule of times.
  Reply With Quote
Old February 14th, 2018, 03:20 AM   #6
Rob...
Supporting Member
United Kingdom

Rob... is offline
 
Join Date: Jul 2016
Location: Manchester
Posts: 142
I know you can get a working backup sometimes if you have an .l5x file with logix 5k.

That's done in an xml format.
  Reply With Quote
Old February 14th, 2018, 03:44 AM   #7
Logix_Stef
Member
United Kingdom

Logix_Stef is offline
 
Logix_Stef's Avatar
 
Join Date: Oct 2014
Location: Havant
Posts: 83
mjellison might be in luck then. I'll have to admit I never looked at the backup features. I just save ste files to disks and USB sticks. Thanks for pointing this out, Rob.
  Reply With Quote
Old February 14th, 2018, 05:12 AM   #8
Hundikoer
Member
Estonia

Hundikoer is offline
 
Hundikoer's Avatar
 
Join Date: Jul 2003
Location: Tallinn
Posts: 271
People with special skills and equipment might be able to read out wiped 0's and 1's. But it is lightyears away from being feasible.
  Reply With Quote
Old February 14th, 2018, 09:22 AM   #9
mjellison
Member
United States

mjellison is offline
 
Join Date: Feb 2018
Location: Amesbury, MA
Posts: 2
http://literature.rockwellautomation...p005_-en-p.pdf

The xml file I have looks very similar to the picture of the l5x file in the document at the link above. Would this backup only work with RSLogix 5000? Is that compatible with a MicroLogix 1400? How would I turn the xml into a .l5x file? Could it just be imported directly into the software?

Thank you all again for your input
  Reply With Quote
Old February 14th, 2018, 10:43 AM   #10
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,387
No, Logix5000 is not compatible with Logix500.

There never was an export to XML with the RSLogix500 software, that only came in with RSLogix5000, but it used the file extension L5X, not XML

I suspect the file you have is not a "backup" of the MicroLogix project.

If you can post the xml file, someone might recognise what it is, the project name, target PL:C etc,
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC 5 memory Latzi LIVE PLC Questions And Answers 11 September 4th, 2012 08:03 PM
omron memory card for plc irondesk40 LIVE PLC Questions And Answers 1 September 30th, 2009 06:19 PM
SIEMENS PLC CPU memory stevenPLC LIVE PLC Questions And Answers 14 April 10th, 2006 10:52 AM
AB PLC 5/80C Memory limit ranjanan LIVE PLC Questions And Answers 6 August 7th, 2003 12:48 PM


All times are GMT -5. The time now is 11:16 PM.


.