PanelView Plus 600
Hello together
I work with a PanelViewPlus 600.
My problem is, that if I wanna set my buttons, there appears the following message
"LatchedPushButton(Name) unable to read from unassigned control"
Can anyone tell me what this message means?
What type of control?
Greets McBacon
Old June 20th, 2013, 07:20 AM   #2
McBacon
Switzerland
McBacon is offline
If somebody could answer me as quickly as possible, it would be great!
Old June 20th, 2013, 08:35 AM   #3
Geospark
Ireland
Geospark is offline
Geospark's Avatar
Quote:
Originally Posted by McBacon
Hello together
Greets McBacon
Under the "Connections" tab in the "Properties" window for the latched button there are three control tags:
Value
Indicator
Handshake
Have you a "Value" control tag assigned for the buttons connection? i.e. the tag you want to "Set".
"...I wanna set my buttons..."
Note:
Just to be clear, you are setting a tag in the PLC, not your buttons.
G.
__________________
"A little nonsense now and then is relished by the wisest men".
Old June 20th, 2013, 08:51 AM   #4
McBacon
Switzerland
McBacon is offline
Reply to:
Yes, I assigned a "Value" control tag for the buttons.
Old June 20th, 2013, 09:00 AM   #5
Geospark
Ireland
Geospark is offline
Geospark's Avatar
Have you only assigned a "Value" control tag?
In the "States" tab, are the values for "State 0" and "State 1" at the default "0" and "1" respectively?
In the "General" tab, what is "Latch reset type:" set to?
"Non-zero Value" or "Zero to Non-zero transition"?
G.
__________________
Old June 20th, 2013, 01:03 PM   #6
Operaghost
United States
Operaghost is offline
Operaghost's Avatar
"Read" would seem to indicate it is unable to read the Indicator or Handshake values. This would indicate the fields are either empty, or they contain invalid names. The Indicator property can be unused, but you MUST assign a Handshake tag to reset (unlatch) the Value tag.
OG
Old June 21st, 2013, 04:38 AM   #7
McBacon
Switzerland
McBacon is offline
@ Geospark
1) Yes, they are
2) Non-zero Value
@ Operaghost
Now I can set the outputs, thanks!
But if I set them they reset themselves after some seconds. (Because of the Handshake I think) How can I use them without that they reset themselves?
http://img5.fotos-hochladen.net/uploads/screenshot047bv5d1toluw.jpg
As information: I took latched push buttons so it should work.
Old June 21st, 2013, 10:33 AM   #8
Geospark
Ireland
Geospark is offline
Geospark's Avatar
Quote:
Originally Posted by McBacon View Post
@ Geospark
1) Yes, they are
2) Non-zero Value
@ Operaghost
Ok, OG got there before me but that's what I was wondering as well, you had no Handshake control tag assigned.
As OG mentioned, you MUST use the Handshake to unlatch the button back to state 0. But, you MUST create a separate Handshake control tag.
You have assigned the same tag, "HMI_Test_2\FT_Greifer", to both the Value and Handshake control tags. This will not work I'm afraid.
I'll explain how the Handshake control works for a latched button...
When you press a latched button it changes from the unlatched state 0 to latched state 1 and writes the state 1 value, default = 1, to the Value control tag. When you want to unlatch the button, i.e. the Value control tag, you must use the Handshake control tag to do so.
To determine how the Handshake control tag unlatches the button, under the "General" tab you select which type of reset, or unlatch, you require for the latched button. This can be "Non-zero Value" or "Zero to Non-zero transition".
Yours is set to the default "Non-zero value".
Using "Latch reset type:" = "Non-zero Value":
Handshake control tag must normally = 0
When a latched button is pressed, it changes from state 0 to state 1 and writes the state 1 value to the Value control tag. Once your logic requires the Value control tag to be unlatched, i.e your button unlatched, you programatically write a "Non-zero Value" to the Handshake control tag, usually a "1". This resets the button back to the unlatched state 0 and writes the state 0 value to the Value control tag.
You must also programatically reset the Handshake control tag back to "0" to prevent continuous unlatching.
Using "Latch reset type:" = "Zero to Non-zero transition":
Handshake control tag may = any value
Again, once the latched button is pressed, the state 1 value is written to the Value control tag. When unlatching, the Handshake control tag must be seen to change from a "Zero to Non-zero" value. The difference with this type of reset is that the Handshake control tag can be any value before an unlatch is required. If the Handshake is "0", to unlatch you simply have to write "1", or any non-zero value.
If the Handshake is "1", or any non-zero value, you have to first write "0", then transition back to "1", or any non-zero value to unlatch.
When you navigate to a screen on the HMI, that has a latched button or buttons, the application attempts to read the Handshake tag to decide which state the button should be at:
If using "Non-zero Value" -
Navigate to screen and...
a) If Handshake = 0 and button unlatched, state = 0
You may then press the button to latch, state = 1
b) If Handshake = 0 and button latched, state = 1
The button is already latched, state = 1
c) If Handshake = 1 then button is held unlatched, state = 0
So c) will hold the button in an unlatched state, even if you press the button, it will not latch.
If using "Zero to Non-zero transition" -
c) If Handshake = 1 and button unlatched, state = 0
From c) note that the non-zero Handshake control tag value of "1" will not hold the button unlatched. Only a transition from zero to non-zero will unlatch. So, again you have to write "0" first, then back to non-zero value, usually "1".
Also note, once you navigate away from a screen with a latched button, the application does not continuously read the Handshake control tag. So it's value can be anything, regardless of your latch reset type, while not viewing that screen. Only when you navigate back will the Handshake control tag value be once again evaluated.
So...because you have assigned the same tag to both control tags, and assuming they are both = "0", when you press the button you are writing a state 1 value of "1" to both the Value and Handshake control tags. Because you are using "Non-zero Value" resetting, as soon as the Handshake control tag is written a "1", the button unlatches to state 0 and writes a "0" back to both control tags. You are latching, then unlatching your button each time you press it.
I hope that's clear enough?
G.
__________________
Old June 24th, 2013, 03:23 AM   #9
McBacon
Switzerland
McBacon is offline
It works!
Thank you very much!
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Panelview 600 dhuber LIVE PLC Questions And Answers 0 July 13th, 2010 09:12 AM
Panelview 600 Communication Gap Archon LIVE PLC Questions And Answers 8 December 1st, 2008 08:15 PM
Comm issue between Micrologix 1200 and PanelView 600 edwinmart LIVE PLC Questions And Answers 5 September 13th, 2008 06:37 PM
Panelview Plus 600 reading from SLC5/03 via NET-ENI story... Jawmunji LIVE PLC Questions And Answers 4 June 20th, 2007 11:30 AM
connect to Panelview 600 with ethernet bpoon LIVE PLC Questions And Answers 7 April 13th, 2006 03:45 PM