0-10v Analog output to control VFD
benjie007
Feb 2010
california
22
I just wanted to send a 0-10VDC to my IF2OF2 module
connected to ML1100 (1763-L16BWA) to control a
VFD.
The idea is to input a number on the PVC300 to adjust
the speed of the VFD.
I was stumble in putting my scale together, or would this be
possible? or wrong wiring may be?
Thanks..
Hi
Could you expand a little on your problem please as I am not sure what you are asking.
Now you could look at the scale instruction in ml 1100 I think it's a scl or a scp
Have a look at both and this will allow you to enter speed or htz on the HMi.
Donnchadh
Thanks Don.
am using SCP instruction.
Input: F8:0
Input min. 0
max. 1023
Scaled min. 0
max. 10
Output. O:1.0
The card was configured as raw/proportional.
See pdf below for data formats that should get you close, use the values for your scaled min and max in the "SCP" instruction. PDF is for a 1762-OF4 but I believe they are the same for the 1762-IF2OF2. Do some testing to verify you get the correct voltage out for a given raw data.
Knowledgebase article 18075 ( tech connect required, I don't have one to view it) is for the 1762-IF2OF2 data format values.
Hey guy's, thanks a lot for all your help.
With all the information you shared ,i be able to
see output as i enter value to F8:0. Its good enough
to start with.
Donnchadh was correct of course. I just saw the shifted 12 bit number occupying up to bit 15 and didn't think it through. It's good to actually read.
Click Plc/analog 0-10 v output module/0-10v dimmable led driver. I made a program using multiple drum to create by increment fade in and out led...
1,414
Hi Friends, I have a LVDT for measurement of cylinder stock which output in resistance. How can I connect it to PLC's analog input? If is there...
2,292
Hi guys, I've a field instrument (actuator) using 24V AC, 0-10V. The terminal connection as below: Terminal 1 = 24VAC Terminal 2 = 24VAC Com...
3,954
Hi. I have an application where I going to control a servo motor. The input to servo motor driver card is +-10V. So I have a +-10V output card...
5,634
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
282