We installed Rockwell ArmorBlock 1732E-OB8M8SR modules, and set the ip addresses.
But, in the properties of the module, it is "Owned No" .
How can we make them owned by the plc?
Thank you .
yellow triangle mark in RSLogix IO tree means:
configuration issue
yellow question mark in RSLinx means:
missing or incorrect EDS file
there are two marks in RSLInx:
yellow question mark and red cross mark .
since you mention about status always :connecting , so try to ping your ethernet module and check status in RSLinx and if possible to post two screen shots in General page and Module Info page in module properties in RSLogix.
you said there was yellow triangle with an exclamation point in RSLogix IO tree, so when you right click that module, then select "properties", the "properties" window will show up, we need three screen shots in that window:
"General"; "Module Info" ; "Connection"
those pix will tell us what is wrong with your module configuration issue.
i saw UTC system time: 1/1/1970.... in Time Sync tab.
so please update controller time to the current:
go to "controller properties", then click "Date/Time" tab, update controller time to current.
please post RSLogix IO tree layout as well.
Is the system time causing some issues ?
We noticed that the 1732E network status led is Flashing green ((The device has no CIP connections. The device has an IP address, but no CIP connections are established.))
How can its CIP connection made ?
there is empty in Grandmaster clock section in Time Sync Tab, it means you did setup CIP connection right.
follow the user manual above you should set it up.
Hello, I am stuck on trying to get an ArmorBlock, 1732E-16CFGM12QCR to respond to EIP outputs. My PLC is Panasonic FP0H-C32ET. I Registered the...
137
Hey there, this is my first thread/question, so hello plctalk-community! :yeah: I got a modul-error for the 1732E-8IOLM12R from the ArmorBlock...
2,357
Hey guys, As you remember from a previous post on another topic I am programming a training cell with 5 robots. One of the robots has the above...
1,044
Hey guys I'm programming this training cell as I mentioned in a previous post. Root of this problem is: We installed the above mentioned module on...
2,018
Is Studio 5000 only owned on a yearly basic? I want to buy it, not rent it.
315