1734-AENTR Point I/O

If firmware revision of modules is correct check on a webserver (type AENTR IP address in web browser) if there is an option to change rack size. If there is - change it and give it a try once again.

BTW. Make sure that last module is mounted correctly ; )
 
Don't expect Logix 5000 to actually set the module properly.
Open up RSLinx, right click the adapter, select "Module Configuration" and set the rack size there.

Curious as to why this particular issue? I've always used the Chassis Size dialog in RSLogix to download the chassis size to the 1734-AENT. Is there some tech note or issue that advises against this method. Always willing to learn :)
 