Member
Hi guys,
First post here but i really need your help on this Devicenet communication error. I have 5 electrical panels wired the same way, but one only of them is giving me this issue.
From RsNetworx diagnostic:
(No Read) Address 22, Indramat DeviceNet Slave DKC06.3-3, Device ID Check: Device ID Check error detected. [1]
The 1756-DNB shows at the same time errors #72 then #78. Couple seconds later, communications comes back OK.
The PLC is coded so if this error occurs, production line stops, and it's happening 4 to 5 time/day, sometime more. And it's never the same node. Sometimes there is more then 1. There is 6 Indramat Ecodrive 03 on this network. Nodes are 11-12-21-22-23-24
It's been like that for the last 3 weeks. I isolated the power of the loop on a powersupply. I raised the RPI of the 1756-DNB from 5ms to 10ms (all other 4 panels are at 5ms). The interscan delay is at 10ms also.
Pleasy any help would be appreciated.
First post here but i really need your help on this Devicenet communication error. I have 5 electrical panels wired the same way, but one only of them is giving me this issue.
From RsNetworx diagnostic:
(No Read) Address 22, Indramat DeviceNet Slave DKC06.3-3, Device ID Check: Device ID Check error detected. [1]
The 1756-DNB shows at the same time errors #72 then #78. Couple seconds later, communications comes back OK.
The PLC is coded so if this error occurs, production line stops, and it's happening 4 to 5 time/day, sometime more. And it's never the same node. Sometimes there is more then 1. There is 6 Indramat Ecodrive 03 on this network. Nodes are 11-12-21-22-23-24
It's been like that for the last 3 weeks. I isolated the power of the loop on a powersupply. I raised the RPI of the 1756-DNB from 5ms to 10ms (all other 4 panels are at 5ms). The interscan delay is at 10ms also.
Pleasy any help would be appreciated.