1756 L62S Losing Program v17
waterbottle
Mar 2019
Florida
42
Hey guys,
Been having an issue with a AB CPU 1756 L62S (red safety) randomly losing the program while in run.
Things i have tried or replaced.
Replace backplane
Added more chasis grounds
Replace 24V source to backplane Ps
Replace L62S and slave
Replace all local I/O
Issue happens randomly machine could run for months without happening or sometimes will happen 2 days in a row
Faults present when downloading the program again
Type 14 safety task fault
Code 9 - a non recoverable fault has occurred in Safety Partner
If anyone can help will be highly appreciated.
Thanks in advance.
i have had this happen with several slc 500 and a plc 5.
the plc experiences a brownout (low voltage) condition and starts to shut down.
in the process, the voltage returns to normal and the plc tries to restart.
place a surge suppressor ahead of the plc ( i use corcom).
if that continues, use a constant voltage transformer.
pressed for time, a line went down.
james
I isolated the 24V feed to CpU with spare power supply with battery backup UPS for the supply. Program failed 2 weeks after. Will this power blip affect the safety guarlogix modules that monitor safety I/o. We use the ethernet safety modules to monitor multiple i/o.
Different companies do different things, so have noticed when a constant voltage transformer has been used and the program does not get lost. But have noticed when cheap companies dont CVT the processor rack and power supply and other temperamental electronics and those same programs seem to just go poof.
Its 24V rack feed not 120V
This safety task fault will delete the program and require that the program be downloaded again. That is by design.
The 'book' solution is to replace the safety partner. You've done that without success.
I was going to say replace the backplane, but it looks like you've tried that.
Have there been any program changes before this started? Safety signature still in place?
The program has had few changes mostly online changes to improve the process of the machine (timers added boolean tag here and there). No changes to the safety logic. Processor is safety locked and safety signature in place.
Just kicking this one out again. We have continued to experience this issue sporadically. Will go away for 6 months and them it will come back 3 times in a week. Still looking for any assistance on this.
https://rockwellautomation.custhelp.com/app/answers/answer_view/a_id/629126/loc/en_US#__highlight
Series B 1756-L6xS Controller may power up with no program and minor battery fault logged
ID: IN33491 | Access Levels: Everyone
Looks like it has a problem with losing power or some kind of fault clearing memory for these controllers v14-v19 firmware.
It appears there is a problem with the controller saving memory while in process. It requires power to complete data transfers internally, and if you lose power in the middle of a data transfer, capacitors (or a battery in this case) are supposed to save it from corruption and allow it to complete the transfers. When they don't complete you get corruption and a cleared program i'm thinking.
Same idea when it comes to flash drives and external harddrives being pulled from power before completing file transfers, OR, without being "ejected". you get the corruption of the drive due to writes/transfers not being completed.
Edit: I know you aren't yanking it out in the middle of operation, but it doesn't mean it can't happen under other conditions that can simulate a temporary power loss while being used.
I purchased some re-claimed racks with L62S/B and partner controllers. The safety is locked and I can not download or re-flash without the...
6,080
Hi all, I have an issue with 1756-L62S (revision 20.13) safety lock. We can't figure out who put safety lock on our project. Before I try...
1,029
So when going through creating logs of all our safety signatures for tracking purposes. I found one PLC without a safety signature. This one is...
9,056
Hi guys, We have a LSP whose battery will not keep the program backed up and needs to be replaced. The new LSP is FW Rev 16.20, while the L62S...
3,265
Hello everyone. My question is about a safety tasks, the PLC is on fault due to a watchdog time expired. The solution is very simple, download...
9,892