1761-AIC to SLC 5/05

trsptfire

Member
Join Date
Feb 2009
Location
Western NC
Posts
49
Presently have two old orange screen 1000 PV connected together with 1761-AIC's then to a third AIC in cabinet beside the SLC 5/05, now the panelviews haven't worked in awhile from what I understand and I see why. The AIC beside the SLC has the standard 1747-C11 cable hanging down not connected to anything, can I get the PV's back to communicating with the SLC using what I have with another cable to connect to the Channel 0 serial port and change it to DH485 or should I purchase a 1747-NET-AIC and use Channel 0 as a 232 connection.:unsure:
 
Tell us the complete catalog number of your PV's.

Channel 0 is RS232 and can be configured for DH485.

Do you mean a 1747-AIC Link Coupler? If so it does not connect to a RS232 port.

Use your 1761-NET-AIC+ and configure the port for DH485.

See AIC+ manual below.
 
Last edited:
I'm not sure what the "X" is for, but the "3" part means it's DH485.

See my edited post above.
 
Last edited:
Yes Mickey that is the 1747-AIC link couplers sorry for the wrong number, so I should go ahead and get the AIC+ and use the CP3 cable and configure for DH485 on CH 0.
 
Yes Mickey that is the 1747-AIC link couplers sorry for the wrong number, so I should go ahead and get the AIC+ and use the CP3 cable and configure for DH485 on CH 0.


I think that is your only option. Short of upgrading the PV's to Ethernet.

I'm guessing that SLC5/05 is a upgrade from a SLC5/03, 02 or 01.
 

Similar Topics

I saw another thread similar to my issue but I have different equipment and didn't want to jump on that one so here is mine: PanelView 600...
Replies
7
Views
5,041
Hi, I have an existing piece of equipment it has the following set up 5/04 processor 1761-NET-AIC DH+ port is connected to a PV And the rs-232...
Replies
5
Views
6,326
Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
Replies
13
Views
1,808
I've attached pics, below. I'm in the field right now an am trying to communicate to the Micrologix 1500 through the 1761-NET-AIC (Ugh!) to...
Replies
6
Views
1,956
The manual for the 1761-NET-AIC shows connecting a PC to DH485 network with a 1761-PM-02 cable. Is this done using a DF1 driver set to...
Replies
0
Views
1,073
Back
Top Bottom