1762-IF4 Questions
crono141
Apr 2018
South Carolina
Hey All,
I'm still pretty new to PLC programming, and in particular how to translate Allen Bradley's documentation into real world information.
The 1762-IF4 Analog to Digital converter has a input voltage range of -10V to +10V, and a 15 bit (bipolar) resolution. I'm trying to figure out what this means. 15 bit resolution means 0-32768. So does that mean -10V equals 0? Does -10V equal -32768, or does -10V mean -16384 (with +10V meaning +16384).
I'm having calibration issues with 2 sensors connected to this ADC, because I'm not sure how I should be scaling the input. Please help! Thanks.
Data sheet here: https://elebi.com/wp-content/upload...y/MicroLogix 1762-IF4 Analog Input Module.pdf
I have a 1V-5V sensor. The problem is I don't know what value to set 1V to (3277 or 1638), and likewise, I don't know what to set 5V to (16384 or 8192). If 1V is 3277 then 5V should be 16384 (which is what I'm currently using). However, with these values I cannot get a sensor to calibrate. We've maxed out its calibration potentiometer and are still short of the target value. If I change the 1V to 1638 we can calibrate, but then I should change the max to 8192 (since its a 10V ADC, and I'm only using 5V of it). Doing that would cause the reported values to be way over actuals.
Are you measuring 1v-5v off this sensor. If so adding any length of wire from sensor to PLC will change your readings, as bright676 mentioned most sensors are 4-20ma
Iv'e used 0-10 vdc in the past but prefer 4-20ma because of the repeatability of the scale factor even with different lengths of cable. 1v-5v seems like a poor range for a sensor
Run it through the SCP function block and scale it accordingly, Turn it down all the way a read what you have - then back up use these numbers for your min/max input and then scale with what you want
Thanks. We are using the EWS-RH Temperature Humidity Sensor, wired in the 1-5V mode. Its potentiometers do not allow the output to scale from 1-5, its just an adjustment, so I can't zero and then max the output to see what we get on the ADC. I am using the SCP function to scale the output to real numbers, just don't know what real numbers to use. The manual for the ADC is unclear.
https://www.omega.com/manuals/manualpdf/M3501.pdf
Yes, but it is currently wired to 1-5, and the ADC is set to 1-5, and the product is 800 miles away and I can't get to it to rewire it. All I can do is update the connected PLCs program.
What pot are they maxed out on: P1 is the low end and P2 is the high end, book says never touch P3
I think your original numbers were correct 3277 min & 16383 max if it was calibrated correct. are you reading both humidity and temperature
We have only adjusted P4. When we crank it all the way it does not reach a value that correlates with a second Fluke temperature probe. It needs to go up 3 more degrees F. This is what makes me think there is something wrong with my program scaling, because we ran into this problem with a brand new sensor from the factory (Read 10F low out of the box).
Thanks. I was hoping someone with experience on this ADC would have clued me in to whether I was on the right track. If need be (because of long wire) I can add a correction factor to this sensors output, but before I do that I want to make sure that I have the input scaled properly.
I have 1769-IF4 module and 1766 micrologix 1400 series B controller, when connecting Analogue input in module it's showing maximum values of...
1,688
It seem there is hardware switch and software setting for signal type one the 1762-IF4? I have a project that I inherited, the hardware swtich...
1,918
Greetings to everyone, my question is: How can I Read a thermpcouple typej ona an analog module (1762-if) on an allen bradley micrologix 1400 (rs...
1,323
Hardware: Micrologix 1100 & 1762-IF4 Analog Input Module Problem: I have one 4-20mA transmitter hooked up to I1:0, I am monitoring the current...
3,376
I'm having an issue with an Allen Bradley 1762-IF4 input card on a MicroLogix 1400 series B. The input to the card is a Futek CSG110 strain gauge...
1,736