Thermocouple on 1762-if4?
wabc1234
Oct 2018
Juarez
Greetings to everyone,
my question is: How can I Read a thermpcouple typej ona an analog module (1762-if) on an allen bradley micrologix 1400 (rs logix 500) and convert the signal to temperature?
thanks in ahead
- A thermocouple doesn't measure an absolute temperature, it measure the difference between a hot junction and a cold junction and that module has no compensation for the temperature of the cold junction, and that introduces a big error.
- The voltage generated by a J thermocouple is at most 30-40 mV and with a input module with a range of -10V to + 10V the resolution you have will be horrible bad.
In other words, to connect thermocouples directly to a PLC, you need a thermocouple input module.
Another alternative is to use an intermediate converter/transmitter with J thermocouple input and 0-10V or current output
I am having an issue getting a IY4 to read my thermocouple correctly. We have a R type and K type hooked up and sitting at a known room...