1769-hsc reset issue!
christos_d
May 2008
Athens
I followed the procedure to reset, in both ways.
The first way it to set the preset value to 0 in the CtrnPreset tag in the configuration array, then toggle the Soft Preset bit CtrnSoftPreset in the ladder logic.
The second way is the the 'Load Direct Write' feature. I set the write control value (Range12To15[n].HiLimOrDirWr) and then toggle the Load Direct
Write bit (Range12To15[n].LoadDirectWrite).
Both ways results the same, as a single scan pulse ONS is not enough to change the counter CurrentCount.
When i toggle the bits, i have to check the CurrentCount of the counter, in order to confirm that the value has changed to the one that i need,
either the CtrnPreset tag value, or the write control value (Range12To15[n].HiLimOrDirWr).
This check of the value change confirmation, can take up to 15 seconds in some cases.
This is something that i cannot control.
Please advise of how i can resolve this problem.
Thanks in advance
Christos
I've got an issue with resetting a counter to 0 on a Micrologix 1500 with a 1769-HSC card. The preset is configured in the IO configuration for 0...
4,861
I used 1769-HSC, CompactLogix processor 1769-L32E with incremental encoder to measure sheet length. I need help hot to reset the current count...
4,218
Hello all. I am having trouble setting up my HSC to count pulses from a prox switch. I have it wired to the prox and I see the .InputStateA0...
1,374
Here is my hail Mary pass I have a wheel that produces 33 pulses per revolution. The RPM of that wheel will be anywhere from 25.21 to 62.7 Pulses...
4,706
Hello all. I have an issue that keeps plaguing me. The system has a 1769-L24ER processor and a 1769 HSC card. I am using CH.0 for tracking...
1,469