1769-IQ16 Sink or Source
Tim Ganz
Dec 2010
Dallas, Texas
689
I need to make a drawing for wiring a 1769-IQ16 module. I have a drawing from AB that shows it will do sink or source.
What is the common u.s. method? What's best?
If the minus side of the sensor's DC power supply is grounded to the frame then use 'sourcing' devices (module wired as 'sinking'). If the plus side is grounded then use 'sinking' devices (module wired as 'sourcing'). If neither then it is your choice.
This is to prevent a shorted-to-frame wire giving a false ON condition.
I think sinking inputs and sourcing outputs are the most common US configuration, and this is my preference. A lot of the European and Asian machinery we get has the opposite.
One argument in favor of sinking inputs has to do with the likelihood of a short circuit causing a false signal to your input. With sourcing inputs, you're pulling the input to common (24v-) to activate it. If your machine has the 24v- tied to ground, and the machine frame is also grounded, it creates a lot of surfaces that could potentially short against the signal wire and activate the input. However, in practice it's probably much more likely that the wires inside a frequently-flexing sensor cable would abrade and short together (seen it happen many times) and in that case the sinking/sourcing setup wouldn't make a difference.
I am designing a concrete mixing plant and require about 6 different speed pulses to determine speed of the 6 conveyors. The maximum speed is 3...
1,313
I have a problem with a CompactLogix 1769-IQ16 input card. The card is being used in sink mode, the OUTPUTS of the device connected to the card...
2,062
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
98
I have a CompactLogix 1769-L31 and need to communicate with it. I only have studio 5000 on my computer. However, when I try to start a new project...
398
I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
256