1769-L35E Fault
beethoven_ii
Nov 2006
Central England
409
I'm currently on site investigating a fault on a customer's plc. The machine has been in and running for about 4 years but overnight it appeared to fault. The OK LED was flashing red but other than that everything seemed ok.
I got called to site this morning to have a look and found that I couldn't get online to the CPU. All upload, download and online options were greyed out. After checking the manual it pointed to the memory being cleared and a firmware update needing doing so I proceeded to do this. I browsed to the CPU using RSLinx within ControlFlash and re-loaded with V20.13 firmware. All worked fine but I still have the same issue. I can see the cpu and all the I-O tree in RSLinx using a DF1 driver or an Ethernet IP driver but I have no option to go online, upload or download. I'm suspecting the cpu may be knackered but wondered if anyone has come across similar before and resolved it?
I think the problem may be resolved now. I tried reloading the firmware again and it went into error part way through and now I can't access the plc through RSLinx. I think it has expired, it has ceased to be, as someone famous once said.
I will tell the customer they need a new plc.
I had a similar issue a few months back. Solid RED fault light, couldn't connect to PLC to do anything. I unclamped each IO card to check the connections. No help. Happened to have a meeting with my local AB rep that day and mentioned the issue. He told me to check the end cap module. I proceeded to unclamp the module and it got the PLC running again. Got another end cap module on order ASAP and replaced it the next week. No issues since. Just a thought to check.
I was about to give up and then saw your post so I thought I'd give it a try. I powered down, removed the end cap and then re-attached it. When I powered up again I was able to download the project and now the machine is back in production. Amazing!
Many thanks for the suggestion.
I was told by the user manual and by users that if you have a solid red fault light then the CPU is shot and it needs to be repaired I bought a...
4,911
I have a system with the following: 1769-L35E::1769-PA2::1769-IQ16::1769-OB8::1769-IF4::1769-OF2 I went to the job on Monday and found the...
7,271
Hello, We have had a machine running for the last 10 years. It has 2 x Kinetix 300 drives. Around a year ago, one of the drives failed. We were...
433
Hi, I recently tried to change the IP address of my 1769-L35E Series A, since doing this the MS indicator is flashing red and the NS indicator is...
936
Good morning guys. Im triying to communicate 4 JXC91 with a 1769-L35E AB CPU. I already test the JXC91 with a newer AB CPU using eds files and...
1,468