2x PanelView 300 Micro and MicroLogix 1400

Ken Roach

Lifetime Supporting Member + Moderator
Join Date
Apr 2002
Location
Seattle, WA
Posts
17,483
A Forum member asked a good DH-485 connectivity question in a Private Message and I'm posting the solution to the general forum so I can use an Attachment to show a hand-drawn sketch.

The MicroLogix 1100 and 1400 controllers have a built-in RS-485 port on Pins 1 and 8 of their Mini-DIN8 connector on the Channel 0 serial port. It can be used for DF1 Half Duplex, Modbus, ASCII or DH-485 applications.

These pins were used for 24V DC accessory power on the MicroLogix 1000/1200/1500 so NEVER connect a cable using these pins to one of those controllers expecting RS-485.

The 1763-NC01 cable provides a screw-terminal connection for this port. You can connect these terminals to the Trunk connector of a 1761-NET-AIC for DH-485 networking. Terminals A, B, COM and Shield should be used; consult the 1761-NET-AIC documentation to decide on cable type and termination.

This cable connection allows us to connect two RS-232 only PanelView 300 Micro terminals to a single 1761-NET-AIC and to the MicroLogix 1400 controller's Channel 0 serial port.

The cables for this purpose can be confusing but the cable end types, cable lengths, and part numbers are very well described in the PanelView 300 Micro Installation Instructions, RA Publication 2711-IN008.
 
A Forum member asked a good DH-485 connectivity question in a Private Message and I'm posting the solution to the general forum so I can use an Attachment to show a hand-drawn sketch.

The MicroLogix 1100 and 1400 controllers have a built-in RS-485 port on Pins 1 and 8 of their Mini-DIN8 connector on the Channel 0 serial port. It can be used for DF1 Half Duplex, Modbus, ASCII or DH-485 applications.

These pins were used for 24V DC accessory power on the MicroLogix 1000/1200/1500 so NEVER connect a cable using these pins to one of those controllers expecting RS-485.

The 1763-NC01 cable provides a screw-terminal connection for this port. You can connect these terminals to the Trunk connector of a 1761-NET-AIC for DH-485 networking. Terminals A, B, COM and Shield should be used; consult the 1761-NET-AIC documentation to decide on cable type and termination.

This cable connection allows us to connect two RS-232 only PanelView 300 Micro terminals to a single 1761-NET-AIC and to the MicroLogix 1400 controller's Channel 0 serial port.

The cables for this purpose can be confusing but the cable end types, cable lengths, and part numbers are very well described in the PanelView 300 Micro Installation Instructions, RA Publication 2711-IN008.

It is possible to "see" on RSLinxs, with this configuration and protocols, the three components? (2 PV's and PLC M1400)
 
In that network diagram, every serial port is occupied, so there's no way to connect a PC to the network. The MicroLogix 1400 does not, as far as I know, perform "passthrough" from Ethernet to DH485.

The principal way I can think of to get a computer also onto the network would be to daisy-chain from the DH485 Trunk connector to an RJ45 connector on a 1747-UIC.

There are other possibilities for adding another 1761-NET-AIC and running either the 1747-PIC/AIC+ driver or a 1747-UIC.
 

Similar Topics

Is this the clock battery flat? Does anyone know how to remove the back of the PV 300 micro. Is it possible to replace this battery. AB says it's...
Replies
2
Views
1,163
I have an opportunity to get some more experience replacing an old Panelview 300 Micro. I'd like to hear any advice you have about it. I suspect...
Replies
12
Views
3,299
I lost the manual for this machine built in 2003 and need to put it back together. I have the Micrologix 1200 and PanelView 300 Micro programs...
Replies
4
Views
1,781
I am tying to download application software to a fresh out of the box PV 300 Micro. The first hitch is a prompt that I am running v4.1xx RSLinx...
Replies
2
Views
1,148
I went on a service call yesterday for a Micrologix 1500. An output wasn't activating and they wanted to know what was hanging it up. It was a...
Replies
10
Views
2,813
Back
Top Bottom