4-20ma, hz, dwell, inverse slope.
ghriver
Aug 2002
Earth>North America>US>CA>Hanford
65
I am hoping someone can explain, well actually point me in the correct direction to be able to do the math on an inverse slope. This is was I have.
4-20ma output to a vfd turning an auger. The augers speed needs to be set via dwell time. (The amount of time the product is in the auger).
The numbers:
vfd scaling = 20 - 60hz
analog scaling = 4 - 20ma
ok, the vfd running at 20 hz equates to 53 seconds of dwell time.
the vfd running at 60 hz equates to 18 seconds of dwell time.
so if 20=53 and 60=18 you would think that the middle vfd scale of 40hz would equal the middle scale of dwell. It doesn't.
This is what i got.
20 hz = 53 seconds of dwell
40 hz = 24 seconds of dwell (middle would be 35.5 seconds)
60 hz = 18 seconds of dwell
so the slope i got m=y2-y1/x2-x1 equates to -1.1428571429. But that would be for a linear slope and from what i see in the output the slope isn't linear. Can some one help?
40hz is the middle of the numbers but isn't the middle of the range. 20hz to 60hz is * 3. You found that the dwell at 40hs (twice 20hz) was about 1/2 (53 / 24) the time as it should be. The jump from 40hz to 60hz is times 1.5 so you should see the time go DOWN by a factor of 1.5 (24 / 18). Dwell is the time to go a distance at a certain speed. Dwell is therefor inversely proportional to the speed (hz). The 'middle' hz for 11/2 dwell is about 34.641016151377545870548926830117 hz. (20 * square-root(3))
You could plot your data in excell and add a trend line which will give you the equation of the line that fits the points.
This isn't really an inverse slope thing. An inverse slope is when the slope value is negative. This is an inversely proportional thing.
This means that the speed times the dwell time is a constant. You can use this constant to go back and forth. Don't try and do this in one piece. It can be done but it will tend to make things more confusing. Also, if you had all the physical parameters of the system you could calculate this constant directly. But we will use your imperical data.
The base equation ot get speed from time is:
VM = C/Td
Solving for C we have:
C = VM * Td
Using your data we get:
60 * 18 = 1080
40 * 24 = 960
20 * 53 = 1060
Given the above results I am going to consider the 40Hz data an anomoly and use 1070 as the constant. Substitute this constant into the first equation to get a command RPM. Based on the 1070 conversion constant I would have expected the 40Hz dwell time to be 26.75 seconds.
Now you can take the command RPM and linearly scale it to 4-20 mA. This will have a scvale factor as well as a y-intercept other than zero. I get a slope of 0.4 mA/Hz and a y-intercept of -4mA.
Incidentally, C is a linear feed constant. It breaks down to:
feet of auger/(feet of feed / auger rev) * gear ratio * (motor Hz/motor RPM) * (60 sec/min)
Granted, this doesn't account for any material slip past the auger. However, since the 20Hz and 60Hz dwell times are so close to each other I don't think there is much of that.
Keith
ghriver said:
The numbers:
This is what i got.
Your slope is correct, but to put what the other guys are saying into simple terms, you didn't bother with the offset. Remember, equation for a line is y=mx+b. You need to determine what b is. I believe you forgot about b, which is what threw your number off. Use the point slope method to solve for b, then I think you'll find that your numbers match.
An OFFSET has nothing to do with it. The error was in thinking that a constant (screw length) divided by a linearly changing speed value (Hz) would give a linear value (time). It doesn't.
Plug the requested dwell time into an equation as suggested by kamenges then use the result.
VM = C/Td
C = VM * Td
60 * 18 = 1080
40 * 24 = 960
20 * 53 = 1060
Keith
^^^^^^ Special Thx. :)
Why wouldn't dividing a constant by a linearly changing speed give a linear value? That sentence makes no sense. It should give a linear value. I agree with kamenges method, buy I don't understand or agree with that statement.
You said you agreed with the method as I proposed it. That means you agree that the dwell time is inversely proportional to speed. That means that if I double my speed, the dwell time is cut in half. If this is true I could double my speed nearly infinitely and the dwell time will never reach zero. It just gets smaller and smaller. The exact opposite is true if I cut my speed in half. The dwell time doubles. I can keep cutting my speed in half and my dwell time will keep doubling keeps.
If this were a linear relationship the slope of the curve would be the same at all points. The curve you get from an inversely proportional relationship has a constantly changing slope. Take the simple equation y=1/x.
Look at some pairs and their slopes:
x y slope
0.5 2
1 1
.5
2 .5
.166666666
3 .33333
It is an inversely proportional relationship. The easiest way to see this is to type some numbers into Excel using an inverse proportion and do an X-Y Scatter plot of them. You will see a curve that is assymptotic to the X and Y axes, assuming you use all positive values for X.
While the result changes in a clearly defined way the result is not linear.
Now, the relationship of desired speed to milliamp command is linear and has an offset.
Keith
I am still having a little trouble getting this down. I have tried to find the vm=c/td by searching google to get a little more explanation but havent had any luck. Can someone help me understand this better. I need to understand whats going on because i have to do this for multiple scales and devices.
ghriver-
Your original post covered a couple of interrelated items. I'm not sure specifically what you are having trouble with. At this point you may want to ask some very specific questions about what you don't understand and we can go from there.
The big thing to get a handle on is the inversely proportional relationship between speed and time given a constant distance and how to represent that in equation form. With a fixed distance, if I double my speed my time to travel the distance is cut in half. That relationship holds for all speeds and times (within reason). All the rest is scaling to make the physical units come out.
Keith
I am actually having trouble understanding the math. I am currently only 2 years into my 4 years of college and I am lacking a little in the math department.
For this particular machine i have the following data.
18 seconds of dwell relates to a decimal value of 30840.
53 seconds of dwell relates to a decimal value of 0.
i understand y=mx+b no problem but the inversely proportional relationship i haven't been able to get a handle on.
Its the same as before if the operator requests a dwell of 40 seconds i need the decimal equivalent.
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
284
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
283
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
1,704
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
494
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
798