I have four 4-20ma signals wired to the old wall charts. I want to find a device to convert the signals (or maybe I don't need to convert them?)and move them over ethernet to our AB SLC 5/05 where I will do all of the flow calculations? (Could scale and do calcs) Any good advice as to the best unit to use for this application?
Thank you very much,Deb
They do not want to wire them over to where the PLC is located in another bldg. We have ethernet close to where the 4-20 mA wiring is located.
A 5/05 can't read ethernet I/P I/O. It has an ethernet port, not an Ethernet I/P port.
If you have a Logix processor in the other building with an ethernet module capable of controlling Ethernet I/P I/O, then you could use the Flex I/O as Tom suggested.
You could get a small PLC with 4 analog inputs and put it on your ethernet network, then use messaging to retrieve the data. Something like a MicroLogix 1100 with a 1762-IF4 card added would work. Then you can use the MSG instruction to communicate between your 5/05 and the ML1100
You might look into these:
http://www.automationdirect.com/adc...nator_I-z-O_Network_Interface_Modules/T1H-EBC
They claim to be able to interface to a PC on an ethernet network, but I would expect you'd need a particular driver package to do this.
Also, be very careful adding ethernet I/O devices to a business lan. PC networks don't play well with millions of tiny little PLC packets flying all over the place. You may need managed switches or a VLAN to do this safely.
great idea but which plc can be compatible with he SLC ETH port ?
Micrologix 1100 with a 4ai ?
I love this site for how friendly it is, and the knowledge that one recieves from all of the helpful, smart minds participating in the posts. Thank you all and have a great day.
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
307
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
292
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
1,717
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
507
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
805