4-20ma & VD

I keep thinking that there should be a better, easier fix for the situation where you need to monitor the low currents, but the motor inputs do not switch until the analog inputs see the falling current upon a stopping motor. I think that the motor starter inputs will always lose the race with the DF analog current inputs. The current inputs will see the low current before the starter inputs have time to switch from on to off.

Good luck with it.
 