4-20ma
JWUNSCH
Jan 2012
CT
I'm new to this so it maybe a dumb question but i'm using a slc500 a.b. 0-20ma output to a 4-20ma input on a rectifier how do i scale the plc output to match the rectifier input?
4 = 0, 20 = 20
The PLC has a 0-20mA Output, and the input of the other device is 4-20mA?
In that case you should scale your output between 0-16mA and then add 4mA.
Let's assume that it's a 12bit analog output module. Then
0mA = 0
20mA = 4095 ---> 16mA = 3276 AND 4mA = 819
To make the calculations for the output, work with the range 0 - 3276, and the add 819 before setting the analog output. (You cannot work with 819 - 4095 directly, because thats not a linear function) That way, when you need a 0, you are setting a 819 that is 4mA and your rectifier will understand it as a "0", and the same for the upper limit.
I hope you understand what I'm trying to explain. Good luck!
What is the part number on the card? some cards you can select the output and you maybe able to change the output to 4-20 then its a easier
Just a thought...
It's an allen bradley analog output #1746-no4i module 0-20ma i didn't see anywhere to change it on the module.
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
275
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
277
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
1,696
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
489
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
791