Am I correctly assuming that there is no need to assign the 9300-RADES to a ControlLogix rack, as this device is simply a means for Ethernet access via dial up anyway? Also, I can't add this device within the controller as it doesn't show up in the avilaable modules list.

Thanks,
 
Right, 9300-RADES has no I/O functions so it should not be placed in the I/O tree of the controller.

By contrast, the 1783-series Stratix 6000 and 8000 can be connected for Ethernet diagnostics and port control as though they were I/O modules.

Also remember that the 9300-RADES takes two sequential IP addresses. One if the configuration/status webserver and Default Gateway, and the next is the LAN address it gives to the dialled-in PC. I usually allow it to use 192.168.1.1 and 192.168.1.2.
 

Similar Topics

Can someone give me a quick, blow-by-blow description of what needs to be done to connect to a Compact Logix or Control Logix PLC through an Allen...
Replies
1
Views
1,438
Hello all, Has anyone tried a more economical alternative to the 9300 RADES (Allen Bradley PLC modem)? Thank you!
Replies
4
Views
2,747
Hello All, I have a question about the setup of a 9300-RADES dialout ethernet modem for communications to SCADA system. On one end I have a...
Replies
3
Views
3,203
Anyone ever encountered an A-B Ethernet modem that wouldn't answer an incoming phone call? Any suggestions?
Replies
2
Views
2,930
Has anyone experiencing problems with this device? To me it looks like its a plain piece of sh*t and I'm looking for a replacement from another...
Replies
4
Views
3,978
Back
Top Bottom