A-B 1769-L32E ethernet problem
jazd
Sep 2009
Newcastle
I'm trying to connect to a 1769-L32E over an Ethernet connection. I cant however seem to browse the device properly over a serial connection using RSLinx.
As you can see the Ethernet module isnt showing up so I cant configure it. I can browse down past the "Local 1769 Bus Adaptor" intermittently (sometimes the red cross is there and I cant browse than a few seconds later it disappears again).
Is there something wrong with the device or am I doing something wrong? Thanks.
Are you using a real serial port on your computer or a USB adaptor.
If so which brand? Is the end cap on the PLC and the lever all the way across.
Regards Alan
Yes using a real serial port, no USB adaptor. The end cap is on and the lever is all the way across.
Sorry about the late reply.
The red NS light may mean you have a duplicate address on the network.
Disconnect the ethernet cable and see if it goes away.
I have listed the reasons below the red MS light will be solid red
Held in reset
The controller is holding the port in reset or the
controller is faulted. Clear the controller fault. If the
fault will not clear, replace the controller.
Self-test
The controller is performing its power-up self-test.
Normal operation during power-up. No action required.
Major fault
An unrecoverable fault has occurred. Cycle power to
the controller. If the fault will not clear, replace the
controller.
Good Day Everyone I could use some advice and/or direction on how to connect remotely using my Wifi to a 1769-L32e. I set up the Ethernet/IP while...
1,392
I am using 1769-L32E. but I have the problem about EtherNet Port as follows; 1. When I test RUN this CPU, I/O LED green blinking. but All...
20,277
Hello all, Right now I loaded the firmware (V15) into a new 1769-L32E Compactlogix Controller. So connection between controller and laptop is...
3,029
I just found two old 1769-L32E controllers in the plant that I cannot go online with using my version of Studio 5000 (30.14). I've reached out to...
1,985
Has anyone experienced the following issue on RSLogix5000 (currently on V16) I have a PLC program that has been running on a site for a number...
1,605