A strange experience with PLC5
AB2005
Nov 2006
Lahore
320
Dears,
Today I have experienced a strange thing which I want to share with friends.
We have two PLC5 one (PLC5/40B) at Corrugator machine and one (PLC5/40E) at Flexo printing machine with different I/O modules in rack. I have RS Logix 5 software in the HMI PC of Flexo machine. I arranged two spare PLCs for both machines. I inserted the PLC5/40B in the slot of PLC of Flexo machine (Remember that both programs have different I/Os configuration). After communication, I download the program of Corrugator. I was assuming that during downloading, system would be in fault due to miss-matching of I/O modules but all the steps of downloading completed successfully. Then I go to online and turned the PLC to RUN mode. After that I installed that PLC at Corrugator instead of original PLC and found the operation correct.
I want to ask if it is the property of PLC or it happened accidentally as it happened with me very first time.
your assumption is incorrect for a PLC-5 system ... specifically, a mismatch in the I/O modules will NOT cause a PLC-5 processor to fault ...
on the other hand, for the SLC-500 platform your assumption would have been correct ... specifically, a mismatch in the I/O modules WILL usually cause an SLC-500 processor to fault ... going further, a mismatch in the configuration for the chassis size will also cause a fault ...
and just for completeness ...
your assumption would usually have been incorrect for a ControlLogix system ... specifically, a mismatch in the I/O modules will usually NOT cause a ControlLogix processor to fault - BUT - it is possible to configure the system so that such a mismatch WILL cause a fault ...
yet another example of "one size does NOT fit all" ...
thank you for sharing your experience ...
Hi All, I'm just trying to understand the reason behind something I recently experienced. Background: The system contains 4 CompactLogix...
130
Hello all, I am facing an issue with my Commander SK that I cannot solve on my own, I am struggling on it since several days :confused: The...
1,076
Hi. I'm doing an upgrade of an old 1400e to a new panel view plus 7 standard using ftv studio v 12,which will be communicating to a slc 5/04 via...
2,650
Can someone explain the jumper between the elements? Does it do anything? See attached jpeg.
695
We have an OPC server getting data from a Compactlogix PLC. The PLC also communicates with a Panelview and a couple VFDs via Ethernet/IP...
1,174