We are using Panel View Plus HMI and trying to figure out if we can create a few screens showing network issues. Example: Smart network switch sends SNMP traffic to WhatsUpGold monitoring software. If set event has been detected by WhatsUpGold, it communicates with AB HMI over OPC. Not sure if this is possible or if there is another way to accomplish this. The end result should be alerts on HMI that would show, for example a failed network switch.
If you have managed switches, they may support something like Ethernet/ IP, and then the PLC could read it like any other IO device. I almost always specify switches that can communicate directly to the PLC.
Monitoring the Switch via SNMP, as you suggested, should be possibile as well, although would involve a few steps in between.
We can not alter PLC program per client. Ideally, we would have something like WhatsUp Gold monitoring software to monitor network equipment and have one or two screens built in PanelView to show said alarms.
no, PanelView Plus cannot talk to an OPC server.
If you were running FTView Machine Edition Station on a PC (same software & project, but different hardware) then you could.
If you want to send alarms/data to the PanelView, then you need to add it to a PLC tag first.
We are cutting over a PLC5 to ControlLogix and we ran into some issues with the HMI (FTView v10, Network Distributed). We found that after...
963
I have a brand new AB 1756-L85E, running version 33, that sporadically bumps the programming laptop and the HMI from communicating with it. After...
1,203
Hello, We are looking at a machine upgrade project, for which we will probably use a Do-More BRX PLC + 3 high speed I/O modules, to automate...
714
Hi, I have a doubt about the system architecture shows below: could two master devices install in same profibus network?
2,663
Hi, A customer wan't to connect to my HMI and run VNC on his side, he doesn't however want to connect to my network in the control cabinet. Is...
1,936