I am bench testing a PF753 (20f11nd096aa0nnnnn). I replaced the IGBT's and IC's in the firing circuit. Upon power up, I get the STS light flashing yellow showing inhibit. In parameter 933, bit 4 is a 1, stating the 'database is performing a download operation'.

Can someone tell me what that means and a solution?

Thank you!
 
I am bench testing a PF753 (20f11nd096aa0nnnnn). I replaced the IGBT's and IC's in the firing circuit. Upon power up, I get the STS light flashing yellow showing inhibit. In parameter 933, bit 4 is a 1, stating the 'database is performing a download operation'.

Can someone tell me what that means and a solution?

Thank you!

bit 4 in the status says it's receiving a stop signal, not database downloading. bit 5 is the database status bit.

verify your IO and setup and see if you're missing power to the stop input which would keep it from being ready.
 
Parameter 933 is 0000010000. The 1 should be on bit 5. (database.....) I'm wrong. Was looking right at it. The bit is a 4. (stop)

Thank you.
 
Last edited:
Bits numbers are zero-based i.e. the least significant bit, i.e. x in 0000_0000_0000_000x, is bit 0.

x in 0000_0000_000x_0000 is bit 4.


[whoops. second!]
 
Duh.....you're right. Haha. I was looking right at it and still put 5. So, looks like 'stop'. Thank you.
 
I never repaired PF753 before, but i had successfully repaired one Kinetix350 before. from my experience, if IGBT was shorted, some resistors connecting between drive ICs (driving IGBT) and IGBT and resistors around drive ICs could be damaged (open or changed value).
 
Last edited:
Duh.....you're right. Haha. I was looking right at it and still put 5. So, looks like 'stop'. Thank you.

No problem we've all done it at some point. Most of the time I'm not using the HIM to determine problems anyway, i'll hook up to the drive 99% of the time with drive executive or CCW and just look through everything quicker.
 

Similar Topics

How to remove faceplate from power flex 753 and not shutting the system down. What parameters should i change?
Replies
1
Views
106
Hi all, I am having a problem with a powerflex 753 we have on site and keep getting input phase loss. The drive has been running for a long...
Replies
7
Views
1,358
Hello Friends, We have a powerflex that stopped working sometime last week. It doesn't communicate over the network, or use CCW directly from my...
Replies
1
Views
455
Hello all! I am fairly new to the world of PLC's and this forum, so I apologize for my lack of knowledge. I have a Powerflex 753 that keeps...
Replies
6
Views
561
Hi, I'm working on a project (AB PLC, L85 v34) where we'll have 20 motors installed, all controlled by powerflex 750 series drives. We need...
Replies
1
Views
962
Back
Top Bottom