Active output while in "Run" on L32E
dburnum
Oct 2008
SW Kansas
163
So i usually don't have problems with my Logix gear, and I'm most likely overlooking something. I have an AB L32E processor, with a 1769-OA8 in the [1] spot of the bus. the #1 channel indicates not active while in stop, or program mode, but as soon as the processor is placed into run, it is active. There are no tags aliased to the channel, and the "module properties"- "Fault/Program Action" are set to "Off". There are also no forces present in the processor. Its not affecting right now, as the implementation of equipment to the module is not installed, but I will need the channel eventually. What am I missing?
Check the actual table for this output. If the bit has a 1 and there is nothing programmed to address it then there is nothing to turn it off.
Thanks, Bernie! That was it. Knew I was just overlooking something, but for the life me couldn't see it.
Doug
I am currently working with a machine using rslogix 5000 and have 2 rungs that are not active yet the output is. These are simple rungs with a...
4,050
Hi there, I have a 4-20mA signal duplicator that has 2 active 4-20mA signals. Unfortunately my PLC input card is also active. If I reverse the...
1,301
I was looking for this function, so that i doesn´t need to do it in the PLC. If there are an alarm in the alarm list, i want to flash the...
544
Context: PLC= S7-1212C, HMI=KTP1200 Basic. Hi again, When the "REPORT" button is pressed (on a different screen), it takes the operator to the...
681
Good morning, I'm new to PLC and HMIs, and I was given the following problem: I need to be able to filter alarms and events that are only related...
394