Good Evening ,
One more question about the Altivar 320 3 Hp . I would like to use the drive’s
24 vdc power supply to energize a 24 vdc contactor . Do you think that a contactor would be too much for that power supply ?
Thanks so much .
Yes. It probably will be too much. Even if it isn't too much the noise from the inductive kick from the starter coil shouldn't be allowed to get into your drive. DC coils should all have flyback diodes to take care of the inductive kick.
Din rail mounted DC power supplies are inexpensive and they provide isolation. For best results I use lots of them. PLC CPUs, network switches, 4-20 ma stuff, and inductive stuff (coils) should all get separate supplies. The accountant that hollers about the cost of the supplies won't be around when a short circuit somewhere causes way too much trouble because you didn't use enough power supplies.
Most of those on-board power supplies are rated maybe 100mA, sometimes less.
For this drive, here are the specs:
+24 Digital input power
supply
I/O +24 Vdc input supply
 Tolerance: –15...+20 %
 Current: 100 mA
Good Evening , I never set up a Altivar 320 Frequency Drive . I must say I never seen a more complicated drive to set up , LOL How do...
2,095
Hi, I am communicating with M241 and few altivars 320, lexiums 32 via ethernet IP and I notice when I disrupt the power supply (turn off the...
2,752
Good Afternoon Guys, I am learning/using Unity Pro S. It is very new to me as most of my experience is with Automation Direct and Allen Bradley...
2,514
All, We have a site that has multiple Altivar 66's that are being controlled by an old Square D Modbus+ network. One of the VFD's has failed...
369
Hello guys, I am trying to control a ATV12 via Modbus Poll software. I need the connection diagram for Altivar Modbus RJ45 port to DB9 port. Thank you
572