Wow , you guys like going round in circles over a small problem !!
Could have all been solved in about 10 minutes !
Assuming the meter reading is OK at 0.004 mA , then we can assume that this is zero - you could stick the test probes in your ear and get the same or more .
Unlikely the device would pass more if reversed in cct
Disconnect the thing completely would show that the input has broken wire or funny scaling .
Simulating the input would prove the PLC side of things , you do have a current loop simulator don't you ?
A couple of PP3's and a meter and you could prove the device . There , 10 minutes - not necessary to take the cooker apart , just considered fault finding
Could have all been solved in about 10 minutes !
Assuming the meter reading is OK at 0.004 mA , then we can assume that this is zero - you could stick the test probes in your ear and get the same or more .
Unlikely the device would pass more if reversed in cct
Disconnect the thing completely would show that the input has broken wire or funny scaling .
Simulating the input would prove the PLC side of things , you do have a current loop simulator don't you ?
A couple of PP3's and a meter and you could prove the device . There , 10 minutes - not necessary to take the cooker apart , just considered fault finding