the following is posted purely for educational purposes and is not intended to be used in any real application
elevmike wrote:
Just out of courisoty, would the following hard wire be considered legal? Using my code above will monator the buttons and provide the output to run the press. However if the PLC output locks on the press still will not run unless both the buttons are pressed.
I understand the timer function would be lost in event of a PLC output lock-on, but still the press wont start without the buttons on.
PLC
OUTPUT
COMMON
* PLC
LH BUTTON RH BUTTON | OUTPUT
-----*^*-------*-------*^*---------*-----||-----*-------(press)
| |
* *
PLC INPUT 1 PLC INPUT 2
Just to be clear, this is a question, not a suggestion.
Thanks,
I have just had to read NFPA 86 which is concerned with Furnace and Oven control and might shed, at least their view, on this situation.
It states, and I'm paraphrasing here, that you can put contacts from a non-safety rated PLC into the safety string so long as they are not connected to the control power source. My reading on that was isolated realays would be what you could use there. Note, that these contacts are in addition to all the hard wired safety contacts which need to be in the string and not in place of any of them. This allows for the plc to enable and stop the burner but the PLC is in no way used to shut down the burner for a field device which has gone out of its safe operating parameters.
In that light, (and now this is a hypothetical of a hypothetical) your connection to the PLC output common could be problematic. Also, as I'm looking at your connection to PLC inputs, it allows for interposing relays on the safety field devices which seems to be how the signals are picked up by the PLC for alarming and display to the operator. A big point is that only one device can be connected to each relay. Like most specs, it does contradict itself on the rating of these relays and in the same sub-section says they have to be rated for combustion duty or that they can be general purpose... go figure.
Other codes can easily contradict this one so this is only one take on how to marry safety items with non-safety PLC's.
This is a 2003 code and it does allow for safety rated PLC's. To meet the code, the PLC must be rated for combustion management so just
any old safety PLC will not do. It also stated that all safety related code must be kept separate from other code. Here my interpretation is that this prevents you from, for instance, de-bouncing a signal that should cause a safety shutdown immediately.
When at the Design Show in Chicago last month I investigated PILZ which does have a safety PLC. They have different application packages (think function blocks) which are rated for different things and they do have a burner management package. You actually pay for these application packages on a per/PLC basis. I even got to meet Thomas Pilz but that paled in comparison to getting to meet Peter (Dr. Loop) Nachtwey at his Auto Tuning presentatoin....