Back to IEC and looking for guidance

testsubject

Member
Join Date
Feb 2004
Location
Chicago, Il
Posts
839
Hi all,

I am getting back to using IEC for schematics and was wondering about the 81346-2:2019 codes.

What does everyone use for a diffuse reflective Photoeye? I am thinking BGB (position switch), but BRA might work as well (light sensor).

What does everyone else use?

Thanks in advance!
 
We use Table 2, which has only 2 letters in the codes. It makes such decisions much easier.
With Table 2 you (and the electricians) have a chance to memorize the codes.
With Table 3 you would have to look up the codes, and that defeats the purpose IMO.
If you go by Table 3, then use BGB.
BGB = "physical dimension sensing object, with boolean output", "position switch".

BRA and BRB would be for detecting light itself, not proximity by light. I.e. for sensing sunlight in a greenhouse.
BRA = "radiation sensing object of visible electromagnetic waves, with scalar output" , "Light sensor"
BRB = "radiation sensing object of visible electromagnetic waves, with boolean output" , "Light detector"
 
lol, electricians memorising codes ?.
Seen what mess they get in when faultfinding.
I know having a standard is ideal if you know it.
One place I did many projects at had their own which was taught to all engineers, but it was the companies own way of identifying plant items.
It also made sense.
for example take a plant with 3 tanks one was called pickles & spreads
So the plant items were like:
MB75-TK01-V001-OPX
So in effect the plant was MB75 (always had plant ident something to do with bottling section) TK01 The tank on that plant, V001 the Valve & OPX the open sensor & so on. The engineers did not need to really know all the codes as they all knew which plant it was & from then on it was obvious i.e. TK01 so somewhere arounf that tank.
Unfortunately, the program symbols could not be documented like that as the limit was 8 chars but the engineers knew what plant they were working on & had to be shortened to 8 chars, however, the itemised labels on the plant were upto 20 chars.
 

Similar Topics

I am trying to deal with fragmented data, and have been getting stuck. So far I am able to command the Fuchs VE Software version correctly and I...
Replies
0
Views
164
I just took a skim through 81346-2:2019 and was wondering which codes you all used for Safety devices like Safety Controllers, EStops, and guard...
Replies
0
Views
562
I know this is a PLC forum but there are many people from around the world that might be able to help me. I have an aspect question (IEC). I am...
Replies
20
Views
2,006
Hi everyone, I'm working on a Mitsubishi Q series PLC whose code was developed in Mistubishi's GX IEC Developer v7.04. I looked online for GX IEC...
Replies
9
Views
1,478
Hi everyone, I'm working on a Mitsubishi Q series PLC whose code was developed in Mistubishi's GX IEC Developer v7.04. I looked online for GX IEC...
Replies
0
Views
501
Back
Top Bottom