Here's a weird one...

There's a Micrologix 1200 in the plant that uses NET-ENI to conect with the rest of the plant network. Lately, I notices occasional PLC timeout messages popping up on an HMI that reads a single word from it.

Today, I decided to replace the ENI with an IAP, which I have found to be infinitely more reliable, assuming it would eliminate the timeouts - it did, but I can't go online with the PLC.

Thinking it might be a minor configuration change, I copied the configuration from another IAP already used on a ML1200, loaded it onto the new one and changed the IP address to match the ENI. It didn't help.

Next, I tried replacing the IAP with the original ENI. The PLC timeout on the HMI returned, and I still can't get online through the ENI.

Lastly, I swapped the ENI with the IAP connected to the other ML1200. Still can't get online with the PLC.

I can get online through DF1 driver and serial cable.
Suggestions?

I havent changed network switch yet...
 
You may have caused a network switch to become confused. I think some of the smarter network switches like to keep arp tables with mac-ids and associated IPs and they don't like it when stuff don't jive no more. That is my highly technical understanding of why sometimes I Have to power cycle a switch to recover
 
Well, I ruled out the network switch - installed a brand new one and I still can't go online with it. Going to try a few other things tomorrow...
 
Is there a lot of traffic hitting the little controller serial port via the LAN? Maybe there is not enough bandwidth to let you get online? If you can disable other devices from trying to read/write to that PLC while you get online maybe that will help?
 
Last edited:
Restart your network switch. works wonders =)

Restart? I doubt that's any more effective than replacing it with a new one.

To answer Okie's question, the only traffic on the PLC is created by a single HMI reading one word.
 
Read too fast X_X sorry rguimond. I don't know if this could be related or not but when you switch out configurations on your controller ie drivers wouldn't you need to restart linx? Because your computer is looking for that certain driver that would fake out rslinx and the driver is their but it says that it isen't their and so on the confusing AB serial train we go.
 
Restarting RsLinx did the trick. I forgot that we are using RSLinx Gateway. I restarted RSLinx on the server and it picked right up.

Thanks for the suggestion!
 

Similar Topics

I'm trying to verify a project with a PLC. The Transfer Setup menu item is grayed out and every time I click Verify with PLC, I get an error...
Replies
1
Views
58
Hi. I’m trying to upload program from existing PLC S7-1200. Create new project in TIA v15.1 then upload. After upload successfully, go online but...
Replies
5
Views
232
Does anyone know of a way to detect if someone is online with the controller in ControlLogix (from logic) I'm thinking that maybe there is a CIP...
Replies
7
Views
390
Got a VIPA 315-2AG23 that i try to go online with but can't seem to make it work through a network. I can go online if i'm plugged directly in the...
Replies
4
Views
275
I'm getting the Dreaded "Failed to go Online with the Controller, Unable to Open Connection - All Connections may be in use" I suspect an...
Replies
7
Views
486
Back
Top Bottom