"CIP ERROR CODE 0020 Insufficient resources"
asim_rana
May 2005
50
We have purchased Controllogix system for our white cement plant at Kohat. And we are facing problem in communication since we purchased it.
Our WonderWare "Intouch" MMI communicate with
controllogix5555 through Ethernet 100mbps "1756 ENBT Module" on "DASABCIP" protocol but controllogix 5555
M16 controller give error message "CIP ERROR CODE 0020 Insufficient resources" for which I had searched all the manuals and help but didn't find any thing about it except this error code in help but with out any details. This message appears when number of communication tags exceeds from 4500 approx and our requirement is 8000 communication tags. This error disappears if we reduce number of tags from 4500 or if all the hardware "Modules" is not configured.
Time overhead slice is 21% for project another also I have noticed that when we configured our hardware with RSNetworx for controlnet then Processor "Estimated I/O Memory" consume all the memory allotted for it.
Details of Memory are below
Total 229,376 bytes
Free 6948 bytes
Used 222,428 bytes
Max used 222,428 bytes
Largest block free 6948 bytes
Estimated Data & Logic memory
Total 3,702,784 bytes
Free 3,463,616 bytes
Used 239,168 bytes
Max used 239,168 bytes
Largest block free 3463616 bytes
Estimated Logic memory
Total 4,194,304 bytes
Free 3,255,940 bytes
Max Used 978,364 bytes
Largest Block free 3,255,940 bytes
Dear Experts We are using 3 control logix systems (3 controllers for three different areas) on a cement plant. On two Ares tags are almost...
2,537
I'm having some trouble with accepting an online edit for a program running in Studio 5000. I'm trying to change the source of a MOV function and...
1,811
I've setup another VM with KEPServerEX but it will not talk to the same PLC that the other is. It is seeing the PLC as it will show another error...
2,468
MicroLogix 1400 Using Messages to talk to PowerFlex 40P 22E-Comm Card. I have it working and when I download an updated Program (nothing in the...
2,417
I have an application with CIP motion drives Kinetix 5700 where I need to set the exceptions for "excessive position error" and "excessive...
1,052