Class 1, Division 1, Help
BudW
Sep 2005
Detroit, MI
107
All,
I am working on a quote for a test fixture that will be located in a Class 1, Division 1 area. Our part of the quote is for the End Of Arm section of what looks like a pick and place unit. The EOA will have a few proximity switches on it. These NAMUR style proximity switches and intrinsically safe barriers will be supplied by others. The proximity switches will be located in the Class 1, Division 1 location. The intrinsically safe barriers will be located in the main enclosure and in a safe area. The proximity switches have a quick disconnect and is using a hazardous NAMUR location cordset. The proximity cables will be pulled into a junction box enclosure and then on into the main enclosure.
Q. Do I still need a Class 1, Division 1 enclosure & cord grips for the proximity cables??
Q. Can you suggest a manufacture & series of Class 1, Division 1 cord grips?
Thank you in advance.
Bud
If I understand correctly, the enclosure will be installed between the NAMUR prox. switches and the barriers, then you can use a standard enclosure. The I.S. barriers will ensure that there isn't enough current for a spark. So you do not need an enclosure that will contain an explosion.
If you were to take a Panelview Plus, mount that in an enclosure that is purged by a purge unit that takes the environment from Class 1 Division 1...
5,677
What class and division is a boiler room typicaly considered to be in most cases? I ask becasue of boiler chemicals used to keep the ph level...
2,461
If you use a 250 ohm resistor to convert a 1-5 volt volt input to 4-20 ma, would that break class 1 div 2 requirements? assuming that all...
22
8,349
Hi, I'm sourcing for a RS232 to RS485 convertor (Class 1 Div. 2), oil and gas application. We are connecting our Allen Bradley PLC, MLX 1500...
6,381
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
121