Comminication to SLC500/04
Jayden
Dec 2007
camperdown
41
Hi all. I have recently started work for a new customer who is running a SLC500/04 processor on a DH484 network. The connection to the processor is via a 1761-net-AIC converter, using the 9 pin portto the RS232 port on the processor. I need to access the PLC's on the network for breakdown maintenance puposes. My question is can i connect to the network via the mini din port on the 1761-net-AIC converter using a 1747-UIC? Or can i connect via a 1761-pm02 cable to this port? Hope this is enough information for you's to be able to help me out.
You can connect to the Mini-DIN port on the 1761-NET-AIC using the 1747-UIC and a 1761-CBL-PM02 cable.
You will use the DF1 Full Duplex driver in RSLinx as described in the 1747-UIC instructions.
You can also connect from a built-in RS232 serial port on your computer, using the 1747-PIC/AIC+ driver. This driver is more complicated to use.
Both of these methods are for connecting to the DH-485 network using the Mini-DIN port on the 1761-NET-AIC only.
As noted, the Mini-DIN port on the SLC-5/04 controller itself is a Data Highway Plus (DH+) port, not a Data Highway-485 (DH-485) port. It requires a specific DH+ interface card.
Hello People, I need your expertise of Communication problem. I am having a KTP1000 DP and ABB PLC which I need to communicate. Now ABB wants...
3,683
Masters, Does anyone here have an Idea on what BLOCKS to be used to read/write registers using MODBUS RS-485 protocol? I am using Unity PRO XL...
1,924
Dear All I am using licensed Rslinx classic gatway for one of my projects. HMI used is iFIx5.0 and its communication with PLC is through OPC...
6,853
Dear sirs, We have a system of S5 135U and S5 115H .Both PLCs connected to monitors through SinecH1 for Coros LSB application.Programmer cable...
2,216
292