Communicating to 4-wire RS-485
electro89
Mar 2012
Canada
106
I'm trying to communicate an MVI71-MCM (Modbus Card for PLC5) as a master to some slave devices. The MCM Modbus ports can be set to 2-wire RS-485 or 4-wire RS-422. The slave devices are all 4-wire RS-485.
Is there any way to make these talk without the use of some kind of converter? Note: the distance is about 150ft.
This is how I connected the 2 RS-485 devices with no success:
Slave Master
4-wire RS-485 2-wire RS-485
TX+ --------------------\__ D+
RX+ --------------------/
TX- --------------------\__ D-
RX- --------------------/
I changed the wiring and changed the Master to read RS-422, and I started reading values. I know these registers are correct because I changed a value in the slave device and it changed in the PLC. Only problem is the numbers I am seeing in the PLC aren't nearly the same as they are on the slave. Should this configuration work?
Slave Master
4-wire RS-485 4-wire RS-422
TX+ -------------------- RX+
RX+ -------------------- TX+
TX- -------------------- RX-
RX- -------------------- TX+
Ignoring the problem with numbers for the moment, are you getting communication errors?
If not then you need to provide a partial list of expected values versus actual register contents. It may just be a information swap or interpretation problem.
I was not getting any errors, but I was finally able to solve the problem. I changed a setting in the slave device to send integer values, not floating point. Now I am seeing valid readings.
Thanks for the reply.
Dear All Please help me about Below picture problem.PLC not communicating proper.
188
I need to recommend a PC to replace a customer's old Windows 7 computer. The only thing I need to think through is the serial com port to...
21
723
Hello Friends, We have a powerflex that stopped working sometime last week. It doesn't communicate over the network, or use CCW directly from my...
474
Hi All I'm trying to connect two zebra printers to th PLC through Ethernet. I can ping the Printer through my laptop connected to the private...
373
Have a customer that has a running 1756-l83es, communicating to redundant ABCIP IO servers for Wonderware 2020. This configuration has been...
893