CompactLogix L32E PLC need to change its IP
DavidRuan
Sep 2014
Toronto
(n)
I bought a CompactLogix L32E PLC recently and assigned an IP address to it by BOOTP and disable BOOTP/DHCP, the PLC was working.
I want to change the IP address of the PLC now into another one with different Subnet mask and Gateway because I did not have enough IP address in the old subnet. When I opened BOOTP, the PLC did not issue any BOOTP request again and I can not assign the new IP address to overwrite the old one, What should I do and how to do please?
Thank you for help.
Hi and welcome to the Forum!
It cannot issue BOOTP requests since you originally disabled BOOTP/DHCP.
The easiest way to change it is to browse to the 1769-L32E Ethernet Port in RSLinx and right click it. Go to Module Configuration at the bottom, and then to the Port Configuration tab. Set your new IP address, mask and gateway here and click Ok.
Regards,
George
Wes, can you elaborate on that statement ?
RSLinx Enterprise running on a PC workstation should have no effect on the BOOTP/DHCP function of any controller or Ethernet module.
In my experience, the issuance of BOOTP or DHCP request is entirely a matter of the values saved to the Ethernet object inside the device's firmware, and the RSLinx Enterprise service does not, to my knowledge, interfere with the BOOTP/DHCP Server utility.
Two other things you will need to do. First (this one might be obvious) is to add the new IP address in RSLinx (assuming you are using the “Ethernet Devices” driver). Second, in RSLogix5000 you will need to change the path to the PAC. If you’ve already uploaded or downloaded to the PAC a path has been set which won’t work with the new IP address.
I have a AB/PLC 1769-L32E Compact Logix. I am using RS5000 to program the device. However, the RS5000 doesn't have the option for controller...
7,209
Hello . Info: Panelview plus 400 2711P-K4M20D Compactlogix 1769-l32E i make a program in RSlogix 5000 and Factorytalk view for...
1,819
Hello again. I need to flash a CompactLogix L32E from firmware ver15 to 16. It has several Panelview Plus's Series D Rev A, connected via...
2,802
Hello. I am trying to establish communication between CompactLogix 1769-L32E and CompactLogix 1768-L43 using serial port but with DeviceNet (and...
2,778
Respected sir/madam I have CompactLogix L32E And I want to data log into logic . is any module or card require to it. request you guid me and if...
1,403