Components are failing when current "events" happen within panel.
AutomationTechBrian
Jul 2013
St. Cloud, MN
669
I'm a little frustrated with an automated saw on a plastic extrusion machine. It's always been the "trouble child", and it must be operational to produce good, clean plastic sheets. Thus, when it goes down, production comes to an immediate halt. ...and everyone looks to me to fix it.
Just in the past couple of months, we had to replace two transformers (which transformed the 480vac to 120vac and 240ac) at separate times. Then, it had a analog servo card (Control Logix, M02AE card) that went bad, so we replaced it. Then, the saw VFD burned out, and I replaced that. Now... I suspect the servo card has failed again. It happened on Friday, so I'm still waiting to confirm with the distributor's tech help Monday morning.
I'm beginning to suspect voltage/current issues, because when something fails, there is usually a corresponding "event" that precedes it. This time, it was something simple. Here's the email I sent the vendor:
The customer was operating the saw normally when he realized that there was an anomaly in the plastic that would bind the saw up. So in the middle of a cycle, he hit the E-Stop... which we've done several times before without issue. The saw returned to home successfully, but....
When he cleared the E-Stop and reset the fault, the servo SLAMMED the top of the saw against the frame. He called me and I went over there immediately.
Troubleshooting... I found the analog output on the card was stuck with an output of -12.xx VDC. Prior to finding the voltage on the analog outputs, every time I reset the program, the servo slammed the top against the frame and the servo faulted out with an over-current. During the course of the night, I re-started the PLC several times and the output never cleared.
I should point out that the -12 VDC is a level that is unusually high for a "return" motion. Usually, the saw would gently move back to home after a cycle. The -12 VDC causes a fast, violent motion. I can't explain why it's so high, other than the card is faulty.
My question to this forum...
If you were in charge of this saw, and it seemed like electrical components were failing with abnormal regularity, what would you do to either investigate the problem or safeguard the machine?
I should add that the main circuits are fused, and there are breakers on each device within the panel.
Thoughts are appreciated! Thanks!
Brian
No, this was the only time the E-stop was involved. I think the saw's VFD bound up once. The other times I'm thinking the servo drive faulted out with over-current.
...actually, I suspect over-current faults being involved ...Although, that doesn't happen with any other panels I work with. If someone said this to ME... I'd dismiss it. But... this saw is so much trouble, it makes me wonder.
It's certainly a possibility. I would guess that the Estop causes the servo to make an immediate stop just like a drive fault would.
Hello everyone, I am working in a platform and we installed FTV CLIENT SE V 12 IN ALL THE CLIENTS COMPUTERS, we have 6 clients and only 1 is not...
106
Hello everyone, I'm having issues with connected components. I got a new laptop and I installed all the RA programs I need without problem. I was...
317
Connected Components Help Hi there everyone, I’m recently new to the PLC world and was hoping somebody might steer me in the right...
447
was trying to use Connected Components to connect to a 525 drive via usb with the face off but can't seem to connect to it. the screen lights up...
804
So I'm using CCW to program a panel view and this is not my first I have done many. My Problem is I get an error message that I have never seen...
507