Your problem is definately more of a mechanical issue rather than controls. The suggestion to raise the temperature of the system is probably the best. However, if your plant is not air conditioned, this senerio will not work during the summer since the dewpoint will be high. The recirculation loop that you speak of, I am guessing, is rather large therefore it will take some time for the loop temperature to rise due to heat generated from pumping and insulation losses. Anything that you do to raise the temperature during recirculation such as an external heater will result in longer startups since my guess is that chilling is essential to the process. The only other viable alternative is to actually shut recirculation when the machine is not running. The system will heat somewhat during the downtime and will require some delay during start-up. But this senerio is possible with the system as designed.