configuring STEP7 (IM151-7 200s) for MPI...WHERE???
oregonsam
Apr 2003
Oregon
65
I can't find a option to make my 151-7 configuration connect to the MPI network in Netpro. It shows a Profibus DP at 3, but I can't connect the CPU to the MPI network.
HELP?
Hi oregonsam.
You set the IM151-7 to MPI in the HW Config program, not in NetPro.
In HW Config, click on the X1 index, the Properties of the port opens up, then change Interface Type from Profibus to MPI.
I only see an X2, not an X1. And when I click it, it doesn't have a selection for MPI. Do I have to type it in manually?
Check type of your IM151-7 and select right one in your HW Configuration. Older models are only able to work as profibus slaves. In HW config they have ony X2 interface. New models can work with Profibus/MPI and they have X1 an X2.
Oregonsam
Does your hardware configuration look like this:-
In my hardware configuration (above), X2 is shown but is unselectable, only X1 can be selected and configured.
Can you zip up tour project and post it here, so that we can load it up and hopefully discover your problem
Paul
I found part of the problem. I was using an earlier version of the CPU in the HW configure...which didn't accept MPI. Now, I just have to figure out how to load the program to the PLC.
Hello all and happy Friday, I'm curious if anyone here has experience sending data over an Anybus Bolt II (HMS AWB6001-A) using a Compact Logix...
774
Hello everyone, I am looking for an easier way to configure all my IO for an OPTO22 PLC. I am developing in Codesys I have a GRV-EPIC-PR1 with a...
587
Greetings to all. We have SST-SR4-CLX-RLL (Molex Modbus module) in remote backplane. The remote backplane, containing SST-SR4-CLX-RLL module, is...
654
disclaimer- 1,no one in their right mind would pick this configuration but I want to try and get it working. 2, my MB knowledge is sketchy at...
1,146
When configuring redundant ethernet cards, will the mac address change along with the IP address. A friend is having problems with IP security...
1,267