Engrtalha said:
... .Currently i m in search for download link of rs Logix 5000 v 7.2 (Grace period).it would be quite helpful for me if any one could share the link.
You are not paying attention in class!...
-Geospark said:
...The prompt clearly tells you the controller is at firmware revision 7.2 and so will require v7.x of RSLogix 5000. Thirdly, it is v7.02 of RSLogix 5000 that you require, and not v7.2. Again, the all too often seen confusion and mix ups between firmware revisions and software versions...
You require RSLogix 5000
software version 7.02 so you can work with a 1756-L1 processor that is flashed to
firmware revision 7.2. They are not the same number! I know you'll get it, eventually.
Engrtalha said:
Secondly is this possible to convert the program that was originally build in ver 7.2 (you mean v7.02!) to any other version like ver 20.0 or ver 16? because i have version 20.0 installed and 5550 series is not present in this version .or should i upgrade both PLC firmware and also original program so that it can open on other version?
More "revision" required!...
Geospark said:
...5550 is a family catalog number of which there is only one member, the ControlLogix 5550 1756-L1 controller...
...The 1756-L1 is the oldest and first ControlLogix processor. It supports firmware revisions from r1.81 up to r13.40...
The ControlLogix 5550 1756-L1 processor cannot be flashed to any firmware revision higher than r13.xx. So firmware revision r20.xx cannot be flashed to this processor. If firmware r20.xx cannot be flashed to this processor, then RSLogix 5000 v20 software cannot be used with this processor. This is why the L1 controller is not present in v20 software. The same can be said for r16.xx and v16.xx, seeing as you mentioned it. Nor can 19, 18, 17, 15, 14. You get the drift?
The latest version of RSLogix 5000 that you can use with this controller is v13.xx. You would have to get a copy of both the v13 software and r13 firmware. You will have to flash upgrade the processor to firmware revision r13. Then you can convert your project ACD file from v7 to v13 and download. It is also possible to convert the project first and when downloading it to the processor it will prompt you to perform the firmware flash upgrade, providing you have the firmware files available on your workstation.
While procuring a copy of the older "RSLogix 5000" v7 is a little bit of hassle, you can download any of the "RSLogix 5000 Enterprise Series" versions, from v10 - v20, on the Rockwell Automation downloads page, again, providing you have a valid license for your current RSLogix 5000 v20 copy.
Regards,
George